V

vickery1971

Hello, I’m after some more advice on my first rewire, it’s in relation to a under floor heating in the bathroom, firstly should I take the power from the upstairs ring, or run a separate feed to it? (the bloke only decided he wanted it today and most of the cables are already plastered in)
Also where can I site the room stat? I had planned to put an isolator on the outside next to the fan isolator . . . . is there anything I should be wary of?

Thanks again for any advice

Ian
 
power from ring via FCU.or on it's own circuit. controller adjacent to bathroom door ( outside, as the sensor is wired fron the controller to the heating mat). ideally mount FCU and control unit at a level whereby the LCD display can be read easily. exact location is usually client's preference, as long as the temp sensor will reach the controller. a lot depends on the make and style of the heating system.
 
Thanks for that, its just that it has a floor temperature sensor but it also does air temperature and the destructions say mount in room that the mat is fitted.
The customer says that he bought it specifically to go in bathrooms.

So much for choosing an easy rewire for my first!
 
if its designed to go in bathroom, then fine. golden rule is follow manufacturers instructions. FCU needs to be located in accordance with BS7671. re bathroom zones.
 

Reply to Advice on my rirst underfloor heating in a bathroom in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I
  • Article
Water underfloor heating and epoxy grouts Hello, I did some reading here and there, but the opinions seem to diverge at some point and I am not...
Replies
0
Views
103
istefanov87
I
  • Question
Thanks all. Sounds like I hadn’t completely missed the point on what Part P needs at least. I’m not so much worried about a knock on the door as...
Replies
4
Views
607

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top