Advice on TABLE 41.3 please? | on ElectriciansForums
Discuss Advice on TABLE 41.3 please? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Peterborough
Table 41.3 provides max Zs values based on Uo = 230V. Can this this table be used to assess Zs for Uo = 110 v ac on a reduced voltage system. Perhaps reducing Zs pro rata?
Thanks for the excellent information. I realise that the 110 volts relates to 55V between the line and centre tap of the output of the transfer providing the reduced low voltage. Table 41.6 for a Type C breaker at 50 A does specify 0.10 ohms. This is about a quarter of that for the same breaker in a low voltage circuit (as I had suspected). In fact in the previous version of BS 7671 it was exactly a quarter.
Thanks again for taking the time to explain.
Reply to Advice on TABLE 41.3 please? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
On a small generator I wouldn't want to risk using diversity as they are not quite as forgiving as a mains supply and can very quickly fail when...
Thank you for your reply. I manage to find the issue I think, the natural and live wasn't inserted properly in one the wago Further down causing...