Hello All,

I am after some advice as I have the opportunity to do some work (upgrading old consumer units) on a couple of empty flats for my next assessment. The trouble is I have never done a Board change in flats before (as I am only a novice), and as usual they are sub boards running from split three phase supplies via old metal box isolator switches with 60A fuses. The cable from the isolators to the boards is 10mm T&E and from the look of it someone ran a 10mm earth to each board too.

My questions are, how do I go about testing ze (it’s a tncs system) as all the earths from all the flats go to a Henley block in 10mm then one 16mm back to the service head, obviously I wont be able to cut everyone’s power to take all the earths out to avoid parallel paths, so any help here would be greatly received?

Next thing is my MEC to the board will only be 10mm, is that a strict no-no or do I just write that on the cert?

Thanks in advance for any advice you can give.
 
Your EIC should just be concerned with the job your doing and so filling in the form should reflect that. Your changing a CU in a flat and that is it, the mains coming into the flat is not your remit and so you do not have to do anything concerning it. Providing there is no obvious signs of damage to the sub main, and your not adding to the loading, which you won't be then just change the CU and do the tests on the flat installation.

As far as the ZE is concerned you do not have to measure it, you can obtain that either by enquiry or calculation. Calculation will not be possible and I doubt enquiry will so I would do a Zs/Zdb, leaving the earths intact and note on your SoTR what you have done, and write on both the EIC/SoTR for Ze the Zs/Zdb and result.
 
Your EIC should just be concerned with the job your doing and so filling in the form should reflect that. Your changing a CU in a flat and that is it, the mains coming into the flat is not your remit and so you do not have to do anything concerning it. Providing there is no obvious signs of damage to the sub main, and your not adding to the loading, which you won't be then just change the CU and do the tests on the flat installation.

As far as the ZE is concerned you do not have to measure it, you can obtain that either by enquiry or calculation. Calculation will not be possible and I doubt enquiry will so I would do a Zs/Zdb, leaving the earths intact and note on your SoTR what you have done, and write on both the EIC/SoTR for Ze the Zs/Zdb and result.
yep...Zdb here malc.....
 
OK gents, thanks for the advice, just me worrying and over complicating things as usual. I will note that I have done Zdb instead of Zs on my EIC and SoTR and see how it goes. I am basically trying to do different things when im assessed each year as I figured if I don’t try different scenarios then I wont learn . . . . fingers crossed!

Just a quick question on the 10mm T&E with 10mm MEC . . . I take it I just state that on the cert? . . . or is it perfectly ok?

Thanks again for the advice!
 
Yes, there is 10mm from the Henley block running to the DB (16mm from Henley to service head) Gas is bonded where it enters the building for all the flats (from Henley to each meter box in 10mm, continuity confirmed visually) Water bonded in each flat, in 10mm from DB, and I could if need be bond the gas as it enters the flat.

The 10mm T&E feeding the board appeared to be only bonded at the DB in the flat, there is no earthing from the Henley block to the metal isolator box containing the 60A cut out fuse.
 
Malc
What does SoTR stand for. Sorry but I'm a bit behind with acronyms.

Great thread Vickery !
 
Thanks, im not sure its such a great thread but I think it’s the setup I see in most of the flats I work in so worth a debate!
 
Last edited by a moderator:

Reply to Advice on testing . . . please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Article
Rather than covering the issue, find where the moisture is coming from and address from that end, is the outside ground level above the inside, is...
Replies
1
Views
242

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top