What form do i need to need to use if i replace a mains board. and also there is no bonding to incoming water and gas and customer will not pay to have it done. what do i put on test certificate. cheers
 
What form do i need to need to use if i replace a mains board. and also there is no bonding to incoming water and gas and customer will not pay to have it done. what do i put on test certificate. cheers



If the customer won't have the 'Bonding' installed/renewed, then you don't do the board change - simple as.:)

6. Main earthing and bonding and
meter tails
6.1. The installer must verify, as a minimum, that:
a) the main earthing terminal of the installation is
connected to an adequate means of earthing
via a suitably sized earthing conductor,
b) the main protective bonding is adequate, and
c) the meter tails and the distributor’s equipment
have adequate current-carrying capacity.
Note. Some electricity distributors have requirements regarding
the earthing conductor, main bonding conductors and meter
tails that exceed the requirements of BS 7671.
6.2. If any of conditions 6.1 (a), (b) or (c) is not met, the
customer should be informed that upgrading is required.
If the customer refuses, the installer should not proceed with the replacement of the consumer unit.


You beat me, Len;)
 
Last edited by a moderator:

Reply to Advice on testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
561
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
935

Similar threads

A
  • Article
What torque is a gas meter test nipple tightened too? What torque is a gas meter test nipple tightened too? What torque is a gas meter test...
Replies
0
Views
245
Anthony1128
A
M
  • Article
Heatrae Sadia multipoint 50 issue? Hi folks I’ve never installed or maintained the water heater above but today I’ve isolated the cold into the...
Replies
0
Views
139
macka09
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top