So my dad was asking my advice about some changes he wants to make to his house electrics.
He wants to add 10 down lights totalling 500w to his existing lighting circuit. Their is one existing lighting circuit on a 5 amp fuse (old type), which has a total of 14 fittings on it already. I worked it out at 100w per fitting, total 1400W which is 5.83A.
So I suggested that he would need to put the additional 500w lights on a seperate breaker, or split the lighting circuit in to upstairs and downstairs to be on the safe side. Either way he would need a qualified electrician to renew the old fusebox and carry out the work.
So anyway, he gets a qualified electrician in to look at the job, who says "nah you can just put all those lights on the exisiting circuit, you will never have all the house lights on at the same time anyway". He quoted him ÂŁ300 to put in a new consumer unit.
Not only that, there has never been any earthing in the bathroom, and to this he says "you wont need any earth bonding in the bathroom, because it will be an RCD unit installed, and the CH and water pipes are earthed elsewhere".
This sounds like BS to me. I dont see how he can say that there is no need for equipotential bonding without checking the resistance to earth of all exposed metal work in the bathroom????
Im not a qualified sparky but I think he is wrong on both points. Can any one please confirm?? I dont want my dad to end up getting ripped off.
Thanks, Jon
He wants to add 10 down lights totalling 500w to his existing lighting circuit. Their is one existing lighting circuit on a 5 amp fuse (old type), which has a total of 14 fittings on it already. I worked it out at 100w per fitting, total 1400W which is 5.83A.
So I suggested that he would need to put the additional 500w lights on a seperate breaker, or split the lighting circuit in to upstairs and downstairs to be on the safe side. Either way he would need a qualified electrician to renew the old fusebox and carry out the work.
So anyway, he gets a qualified electrician in to look at the job, who says "nah you can just put all those lights on the exisiting circuit, you will never have all the house lights on at the same time anyway". He quoted him ÂŁ300 to put in a new consumer unit.
Not only that, there has never been any earthing in the bathroom, and to this he says "you wont need any earth bonding in the bathroom, because it will be an RCD unit installed, and the CH and water pipes are earthed elsewhere".
This sounds like BS to me. I dont see how he can say that there is no need for equipotential bonding without checking the resistance to earth of all exposed metal work in the bathroom????
Im not a qualified sparky but I think he is wrong on both points. Can any one please confirm?? I dont want my dad to end up getting ripped off.