Gone to a job this morning had a call from a customer when i plug too much I'n on this side of the kitchen it trips the whole house, house DB protected by 30ma rcd. Went to the job apparently this has been the case for 4 years or more. Happens then washing machine is on and toaster and kettle is used. Trip it now appears that 2x sockets on one side are on the ring. Over the other side on t&e goes down the wall to feed a socket above worktop, spur from this to under cuPboard lights, spur to socket below worktop to wm outlet, spur from this to tumble dryer, spur from this to double socket on worktop further over. Bingo! Problem solved overloading one t&e radial, from ringmain, must be jb above ceiling! All faceplates nackered a right mess under cupboards t&e lashed everywhere and you should only spur off once I've said best option is to run a new circuit. All old stranded cable however insulation resistance tests all good etc. Just to sort it all properly. It will take me a day on my own to complete and test, dabbing new ring into existing board surface trunk above units then drop behind units for 5 double sockets and 3 spurs for appliances. Was going to go I'n at 400 pounds does this sound fair ?