Hi all first post so please go easy on me. Just to give a bit of background on myself I have been qualified for 12 years and have recently completed my 18th edition and 2391.
I’ve recently been carrying out an EICR on a MOD industrial waste water treatment site.
The question I have is about a supply to a Nissen hut style building. The main site supply is TNCS with a feed coming from the MCC to some overhead lines (TPN&E) which then feeds (SP&E) the Nissen hut. It then goes to an enclosure on the post with an 100mA rccb then to a 40A MCB. It then goes from there in singles in galvanised conduit to the hut which has an externally mounted DB with a 30mA main rccb on it. The building is a good 50M from the MCC.
I’ve given a code 2 on the fact that there is no earth electrode at the hut due to the fact it has a corrugated metal roof which can be touched with a possible difference in potential to earth. Do you think this is correct?
I should add that all Zs and RCD results were acceptable.
Thanks
I’ve recently been carrying out an EICR on a MOD industrial waste water treatment site.
The question I have is about a supply to a Nissen hut style building. The main site supply is TNCS with a feed coming from the MCC to some overhead lines (TPN&E) which then feeds (SP&E) the Nissen hut. It then goes to an enclosure on the post with an 100mA rccb then to a 40A MCB. It then goes from there in singles in galvanised conduit to the hut which has an externally mounted DB with a 30mA main rccb on it. The building is a good 50M from the MCC.
I’ve given a code 2 on the fact that there is no earth electrode at the hut due to the fact it has a corrugated metal roof which can be touched with a possible difference in potential to earth. Do you think this is correct?
I should add that all Zs and RCD results were acceptable.
Thanks