Sorry I don't know how to post up a youtube link but have a look at the John Ward one part 2 on AFDD's worth a watch.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss AFDD !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! in the UK Electrical Forum area at ElectriciansForums.net
Thanks Anthony for the very informative post....probably need Michael more on the case
Not really informative mate. The test was a farce.. Read post #15
It is quite alarming how these false videos are just taken as gospel by people as if millions of pounds of research would be wrong but an anorake in a shed with crap equipment is correct.
If, the maximum fault energy to cause a fire is required to be limited by an RCD to 0.3^2 x t, then why is it allowed to be 2.5^2 x t for an AFDD?
I know, I have access to the standard.Just to put it into context, if it was a 32A AFDD then it would be about 5A
You are correct, in that RCD's do not protect against series faults, such as broken conductors, we have MCB's to protect against L-N faults.J.W. has just posted the third video with an electric heater and it still did not trip. RCD's are ok for faults to earth not sure regarding L-N and broken conductors. Look forward to the replies.
A 300mA RCD is not going to trip in the event of a fire, until the cables have melted enough, to allow earth leakage to occur.Don't forget, I mentioned nothing about additional protection by RCD, i.e. a 30mA device, I was referring to 0.3A devices, 300mA, for prevention of fire, as per BS7671 clause 422.3.9.
Reply to AFDD !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! in the UK Electrical Forum area at ElectriciansForums.net