TL.DR version. AFDDs are a crap solution to a problem we don't have, use an RFC and forget about them.
In more detail..
From IEC62606-2103
"Residual Current Devices (RCDs) are recognised as efficient to reduce the risk of fire by detection of leakage current and arcing to ground as a consequence of tracking currents within an electrical installation. However, RCDs as fuses or circuit-breakers are not able to reduce the risk of electrical fire due to series or parallel arcing between live conductors.
During a series arc fault, there is no leakage to ground therefore RCDs cannot detect such a fault. Moreover, the impedance of the series arc fault reduces the load current, which will keep the current below the tripping threshold of the circuit-breaker and the fuse. In the case of a parallel arc between phase and neutral conductor, the current is only limited by the impedance of the installation. In the worst cases of sporadic arcs, the conventional circuit breakers were not designed for that purpose."
And the test procedure from IEC62606-2013..
"The insulation across both wires is to be slit 50 mm (or 2 inches) from one end to a depth to expose the conductors without severing any strands.
d) The slit in the insulation is to be wrapped with a double layer of electrical grade black PVC tape and overwrapped with a double layer of fiberglass tape.
e) The conductors are to be stripped at the end farthest from the slit approximately 12 mm (or 0,5 in) for connection to the test circuits. The cable specimen shall be then conditioned to create a carbonized conductive path across insulation between the two cable conductors:
f) The cable specimen is to be connected to a circuit providing 30 mA short circuit current and an open circuit voltage of at least 7 kV. The circuit is to be energized for approximately 10 s or until the smoking stops.
g) The cable specimen is to be connected to a circuit providing 300 mA short circuit at a voltage of at least 2 kV or sufficient to cause the current to flow. The circuit is to be energized for approximately one minute or until the smoking stops."
AFDDs are an attempt to reduce fires in timber buildings using relatively high-current radials, in North America where poor termination and/or breaks in conductors start fires. In the UK RFC's are inherently tolerant of single faults, a feature that makes them incompatible with AFDDs. Given the choice between an RFC and an AFDD it has to be the RFC, it's a cheaper and much more reliable way to reduce the risk of fire from a broken conductor.