Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed.
The property has passed but there are parts of the report that don't sit right with me and I want to know what my peers think? Am I being ---- or is there something in my concerns. Report is attached with redacted details.
My concerns as as follows;
Date of last inspection -Being a PRS property and (I'm led to believe) the client has used the same people every time - Records should be available right?
Summary of condition notes about minor deviations from BS7671 but does not list them; no point in stating it then right, I mean if you can't list what they are.
Report has come back as satisfactory so from the LL POV, they're unlikely to bother with anything I note but this is for my knowledge rather than anything else
Supply and characteristics
TN-C is ticked as the supply type; I believe this is a typo as the head is a tncs one looped service.
Number of live conductors; AC and Supply polarity are ticked but no phase/wire details recorded.
DNO Fuse is listed as BS1361 60A however it was never inspected, nor DNO contacted, I'm wondering if they have pulled fuse before and know the size or if they're going off 6mm bonding conductors and tails.
Main protective earthing conductor is recorded as 16mm with 6mm main bonding conductors. I take umberage with them being verified as I don't believe this was done (certainly if you look at the under-sink shot I posted in #earthing-and-bonding , it's just a link across the water meter, with no further signs of bonding (haven't checked boiler).
Incorrect BS type in main Switch details. Recorded as a 30mA RCD main switch which is not the case, standard 100A DP Isolator on board. No voltage rating/fuse setting recorded. 27ms trip time recorded.
OBS
Unable to access conservatory lighting feed due to tenant property. - not 100% true or accurate. Conservatory light and power appears to be fed from downstiars lighting and/or power circ hits - I don't dispute the FI code applied.
3.3 514.13.1 - From what I see the clamps have the required 951 labels, no external MET so not sure why he's C3'd it.
3.4 confirmation of earthing conductor size - 542.3 543.1.1 - ticked but as DNO OCPD not verified can't say if 6mm is appropriate or not.
3.6 confirmation of main protective bonding conductor size - 544.1 (as above)
3.7 condition and accessibility of mainbonding connections - 543.3.1 544.1.2
4.9 correct identification of circuit details and protective devices 514.8.1 514.9.1 - No schedule present, incorrect CU labelling, no mention of Conservatory being fed off downstairs lighting/power circuits - Item is ticked
4.11 presence of non-standard mixed cable colours label 514.14 missing yet ticked.
4.13 other labelling (514) - no mention of Conservatory fed off downstairs lighting/power
4.17 protection against EMI where cables enter enclosure (521.5.1) marked N/A - tails enter together in suitable gland - tick instead?
4.21 connections tight and secure - Not a torque driver in sight, yet ticked
5.2 cables supported throughout (521.10.202 522.8.5) marked as LIM but not listed in limitations
5.10 prescribed zones - marked as LIM but not listed in limitations.
5.11 as above
5.17 terminations (526.6) ticked but not a torque driver in sight
6.3 Shaver socket in bathroom comply to BS EN 61558-2-5 (701.512.3) marked N/A even though device is present
6.4 Supp Bonding not present/verified but marked N/A
Just wondering everyone's thoughts? Am I being anally retentive?
The property has passed but there are parts of the report that don't sit right with me and I want to know what my peers think? Am I being ---- or is there something in my concerns. Report is attached with redacted details.
My concerns as as follows;
Date of last inspection -Being a PRS property and (I'm led to believe) the client has used the same people every time - Records should be available right?
Summary of condition notes about minor deviations from BS7671 but does not list them; no point in stating it then right, I mean if you can't list what they are.
Report has come back as satisfactory so from the LL POV, they're unlikely to bother with anything I note but this is for my knowledge rather than anything else
Supply and characteristics
TN-C is ticked as the supply type; I believe this is a typo as the head is a tncs one looped service.
Number of live conductors; AC and Supply polarity are ticked but no phase/wire details recorded.
DNO Fuse is listed as BS1361 60A however it was never inspected, nor DNO contacted, I'm wondering if they have pulled fuse before and know the size or if they're going off 6mm bonding conductors and tails.
Main protective earthing conductor is recorded as 16mm with 6mm main bonding conductors. I take umberage with them being verified as I don't believe this was done (certainly if you look at the under-sink shot I posted in #earthing-and-bonding , it's just a link across the water meter, with no further signs of bonding (haven't checked boiler).
Incorrect BS type in main Switch details. Recorded as a 30mA RCD main switch which is not the case, standard 100A DP Isolator on board. No voltage rating/fuse setting recorded. 27ms trip time recorded.
OBS
Unable to access conservatory lighting feed due to tenant property. - not 100% true or accurate. Conservatory light and power appears to be fed from downstiars lighting and/or power circ hits - I don't dispute the FI code applied.
3.3 514.13.1 - From what I see the clamps have the required 951 labels, no external MET so not sure why he's C3'd it.
3.4 confirmation of earthing conductor size - 542.3 543.1.1 - ticked but as DNO OCPD not verified can't say if 6mm is appropriate or not.
3.6 confirmation of main protective bonding conductor size - 544.1 (as above)
3.7 condition and accessibility of mainbonding connections - 543.3.1 544.1.2
4.9 correct identification of circuit details and protective devices 514.8.1 514.9.1 - No schedule present, incorrect CU labelling, no mention of Conservatory being fed off downstairs lighting/power circuits - Item is ticked
4.11 presence of non-standard mixed cable colours label 514.14 missing yet ticked.
4.13 other labelling (514) - no mention of Conservatory fed off downstairs lighting/power
4.17 protection against EMI where cables enter enclosure (521.5.1) marked N/A - tails enter together in suitable gland - tick instead?
4.21 connections tight and secure - Not a torque driver in sight, yet ticked
5.2 cables supported throughout (521.10.202 522.8.5) marked as LIM but not listed in limitations
5.10 prescribed zones - marked as LIM but not listed in limitations.
5.11 as above
5.17 terminations (526.6) ticked but not a torque driver in sight
6.3 Shaver socket in bathroom comply to BS EN 61558-2-5 (701.512.3) marked N/A even though device is present
6.4 Supp Bonding not present/verified but marked N/A
Just wondering everyone's thoughts? Am I being anally retentive?