Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection.

Was after a larger unit with full RCBOs. Every Sparky I've spoken to has varied in their suggested plans.

1) Some say do an EICR first, others happy to just go straight with a new CU. EICR seems to add a big upfront cost.
2) Some mention DP RCBO, others don't.
3) One said for Building control notification, I've have to check the date on your smoke/heat & carbon monoxide alarm (?).
4) One said gas/water pipe bonding would be required and it's extra
5) One said, I'd have to get an isolator switch fitted by my supplier before the CU can be replaced. Currently there is only a mains fuse for isolation. The CU and mains fuse are both next to each other.

Prices vary for 1, 2, 3 significantly, I mean the most expensive quote is literally double the cheapest quote!

Any advice would be appreciated as this is driving me nuts!
 
Not a main switch in a db, I use a separate RCD main switch which provides back up fault protection in case of rcbo failure, and protects the metal frame of the db rather than relying solely on mechanical protection to the tails.
 
Not a main switch in a db, I use a separate RCD main switch which provides back up fault protection in case of rcbo failure, and protects the metal frame of the db rather than relying solely on mechanical protection to the tails.
If the db isn’t remote from the cut out and tails are properly installed a main switch with dp rcbos is compliant adding an upfront rcd is going to reduce selectivity
 
If the db isn’t remote from the cut out and tails are properly installed a main switch with dp rcbos is compliant adding an upfront rcd is going to reduce selectivity
In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
 
Not a main switch in a db, I use a separate RCD main switch which provides back up fault protection in case of rcbo failure, and protects the metal frame of the db rather than relying solely on mechanical protection to the tails.
If the db isn’t remote from the cut out and are properly installed a main switch and dp rcbos is compliant
In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
sp rcbos on a tt with a main switch would have no selectivity with a N to E fault.

I think the issue is making a statement saying Required or Needed means that there are no other options.
 
Last edited:
In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
You just said it again “ dp rcbos are required”.

Dp rcbos are not a requirement they are an option.
 
I think you are rather mis-interpreting. I have only ever stated that where an upstream s type rcd is used in front of a db with rcbo's single pole rcbo's would not be compliant and therefore by default are required in that situation.I stand by that.
 
I think you are rather mis-interpreting. I have only ever stated that where an upstream s type rcd is used in front of a db with rcbo's single pole rcbo's would not be compliant and therefore by default are required in that situation.I stand by that.
Look at the definition of Required.

Your post @ 34 says sp rcbo with main switch would be compliant?
 
A main switch....not an rcd main switch. A db with a main switch and sp rcbo's would be compliant. It is not the way i would do it though.
Add a s type rcd main switch and the sp rcbo's are no longer compliant.
 
A main switch....not an rcd main switch. A db with a main switch and sp rcbo's would be compliant. It is not the way i would do it though.
Add a s type rcd main switch and the sp rcbo's are no longer compliant.
I wouldn’t add an upfront rcd at all

Dp rcbos with main switch would be much better although not a requirement 🙄
The use of an upfront rcd should be avoided if possible.
 
Last edited:
And - just to throw a spanner in the works!

Regulation 411.5.2 (Just refreshing memory on TT systems) states;
One of the following i) RCD OR ii) Overcurrent Protective Device shall be used, with;

Note 1 "An appropriate overcurrent protective device device may be used for fault protection provided a suitably low value of Zs is permanently and reliably assured."

Now we know in the real world a 'permanently and reliably low value of Zs' is unlikely, but hyperthetically, installing a RCD is not necessarily a god given!
 
And - just to throw a spanner in the works!

Regulation 411.5.2 (Just refreshing memory on TT systems) states;
One of the following i) RCD OR ii) Overcurrent Protective Device shall be used, with;

Note 1 "An appropriate overcurrent protective device device may be used for fault protection provided a suitably low value of Zs is permanently and reliably assured."

Now we know in the real world a 'permanently and reliably low value of Zs' is unlikely, but hyperthetically, installing a RCD is not necessarily a god given!
Irrelevant.
All I have stated is that where an up front rcd is used sp rcbo's would not be compliant. I have not suggested any of the above is required, only the requirements where they are used.
 

Reply to After a New Consumer Unit, now I need EICR & 100A DP Isolation Switch in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
2K
  • Question
Our house in a row was built in 1971 and we have metric cables with cpcs for the lighting, top of the row imperial and no cpcs.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top