Got a call from work to go and visit a signage factory, they manufacture road signs, lights etc. One of their machines is used to buff/sand/polish cylindrical stainless steel pipes. This is a belt sander which rotates via a motor inside the unit, the belt sander is then spun around via a secondary clutch drivin motor.
The machine is plc run. They were complaining of getting shocks off the machine when using it. Their is a visible electric arc between the pipe and the guard and as the belts are nylon its obviously excess static.
So i do a EFLI tests on each Line(3 phase machine) and all readings satisfactory so i delve into the machine and have a high resistance Earth-Line on the 24v system. I found this, can you guys explain the logic? I removed the link Between a transformer and the earth block. Cable 24-0 and the din rail terminal and retested and it was clear. The loose earth as pictured was inside the same terminal as the red 24v outgoing cable the linked to the din rail earth.
The machine is plc run. They were complaining of getting shocks off the machine when using it. Their is a visible electric arc between the pipe and the guard and as the belts are nylon its obviously excess static.
So i do a EFLI tests on each Line(3 phase machine) and all readings satisfactory so i delve into the machine and have a high resistance Earth-Line on the 24v system. I found this, can you guys explain the logic? I removed the link Between a transformer and the earth block. Cable 24-0 and the din rail terminal and retested and it was clear. The loose earth as pictured was inside the same terminal as the red 24v outgoing cable the linked to the din rail earth.