ive just gone round to a friends garage and he has armered comming into the garage but it just goes into a plastic jb with a rubber gland and then onto the ccu. surely this is against regs?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss against regs or just frowned upon in the Australia area at ElectriciansForums.net
The armour will still need earthing as its an extraneous conductive part
Unless the method of installation, is one that is indicated in the cable manufacturer's instructions, then it does not comply with the Regulations.
I'm not aware that cable manufacturer's have ever suggested that a SWA cable should be installed in such a manner, as I understand it, they all recommend the use of an SWA gland, and if earth separation is required, use of an insulating insert, an insulating gland, or an insulating enclosure.