Hi thanks in advance for any advice..
A long story, but have been asked to install new electrics to a new milking parlour on a local farm. The issue I have is that I am convinced the existing supply is not big enough, the existing supply is single phase and is installed about 30m from parlour in a top floor barn ( there are 3 x 25mm sub mains fed via 80A KMF switches( armourdes ) feeding the house, parlour and storage heaters in the house.
The problem I have is the farmer was told by a larger electrical company who installed lights in parlour (ÂŁ4000 for eight low bays with 1.5 days labour which I couldn't believe, however that's another story) that the supply is large enough (apparently used clamp meter while he was milking).
The parlour installers aren't that helpful and won't give me the loading of all their new equipment ( one motor alone pulls 21A at FLC I noticed) , however I have logged the existing parlour and while milking they are averaging 65A ish ( House 10 Amps, parlour 55 Amps), but when compressor etc kicks in it can rise to 90A for short periods. Also I have noticed when milking, the lights in parlour flicker and sometimes turn off
(I have checked voltages at supply while milking and found supply drops from 230V when not milking to 217V so was thinking the ballasts were switching off due to voltage being too low, but not sure). Also could somebody correct if wrong, but was thinking this would cause motors/ capacitors etc to burn out more frequently due to the low voltage.
I keep telling farmer I think he needs new supply, however he wants me to install and check again after parlour has been Installed.
What would be really helpful is if anybody has experienced anything similar before and what would you recommend. In the ideal world I thought he should of had 3 phase supplied and 3 phase motors etc, but it's too late for that now as parlour is installed and is all single phase.
I thought maybe a new single phase to new parlour as couldn't go to where existing is as I think new parlour will still be above the 80A fuse in KMF switch.
Also I was thinking of getting a power quality analyser ( not sure if it would help though) or asking DNO too come out and check existing supply, but not sure of the procedure.
I know it's a random post ( police would consider it a cluster...k I believe) , but just looking to see how everyone else would approach this appart from not getting involved with it.
Much appreciated for any help....
A long story, but have been asked to install new electrics to a new milking parlour on a local farm. The issue I have is that I am convinced the existing supply is not big enough, the existing supply is single phase and is installed about 30m from parlour in a top floor barn ( there are 3 x 25mm sub mains fed via 80A KMF switches( armourdes ) feeding the house, parlour and storage heaters in the house.
The problem I have is the farmer was told by a larger electrical company who installed lights in parlour (ÂŁ4000 for eight low bays with 1.5 days labour which I couldn't believe, however that's another story) that the supply is large enough (apparently used clamp meter while he was milking).
The parlour installers aren't that helpful and won't give me the loading of all their new equipment ( one motor alone pulls 21A at FLC I noticed) , however I have logged the existing parlour and while milking they are averaging 65A ish ( House 10 Amps, parlour 55 Amps), but when compressor etc kicks in it can rise to 90A for short periods. Also I have noticed when milking, the lights in parlour flicker and sometimes turn off
(I have checked voltages at supply while milking and found supply drops from 230V when not milking to 217V so was thinking the ballasts were switching off due to voltage being too low, but not sure). Also could somebody correct if wrong, but was thinking this would cause motors/ capacitors etc to burn out more frequently due to the low voltage.
I keep telling farmer I think he needs new supply, however he wants me to install and check again after parlour has been Installed.
What would be really helpful is if anybody has experienced anything similar before and what would you recommend. In the ideal world I thought he should of had 3 phase supplied and 3 phase motors etc, but it's too late for that now as parlour is installed and is all single phase.
I thought maybe a new single phase to new parlour as couldn't go to where existing is as I think new parlour will still be above the 80A fuse in KMF switch.
Also I was thinking of getting a power quality analyser ( not sure if it would help though) or asking DNO too come out and check existing supply, but not sure of the procedure.
I know it's a random post ( police would consider it a cluster...k I believe) , but just looking to see how everyone else would approach this appart from not getting involved with it.
Much appreciated for any help....