acvc
- Joined
- Jun 1, 2008
- Messages
- 435
- Reaction score
- 26
Happy New Year to all you folks out there. I hope it's a successful one for you all and many thanks for all your help and good advice last year
I was called to a guys's tripping ring circuit today. 32A ring final with BS3871Type 2/Old Wylex BS 3036 board with adaptors/TNCS/Main earth present and 6mm/ Water+Gas main bonding present and 6mm.
No recent building or DIY. The bloke plugged in his xmas lights and 5 minutes later the tripping began (could be just a coincidence). From then on, with definitely nothing plugged in, the MCB will not reset. There is some moisture in a couple of sockets on the ring. I put the conductors in these boxes into connector blocks and taped them up. Then went on to test.
Continuity 0.60 on R1 and Rn end to ends.
Continuity 28 ohms and fluctuating on R2 end to end.
Crossover R1 and Rn 0.30 at all points.
Crossover R1 and R2 variable from lowest 0.25 to 1.72 highest.
Ins Res 0.00Mohm between each three conductors.
Then .... I split the ring middlish and ....
for quick location of short I went straight to INS RES and still says 0.00Mohm on BOTH legs, between all three conductors!
AND neither of the (now separated) legs of the ring trip the mcb.
Put a 16A BS60898 on to activate one leg, and highest Zs on the leg is 0.72.
I am 99% certain that I identified the appropriate ends of each conductor in the board.
Now I'm very very confused. My thoughts are:
1. There's a parallel earth path present AND
2. (Not sure about this but) As two separate radials the Zs on each isn't low enough to activate the MCB. But when joined as a ring, the Zs is lowered (halved) as the earths are now effectively in parallel.
Anyone come across this fault scenario before? Thanks chaps.