An agreed limitation of this EICR is that the air circulation unit circuit will not be inspected beyond the switchgear / controls due to no safe means of accessing units on roof of 4 story building. We're discussing how to resolve this. In meantime:

I'm inspecting the air circulation supply at the intake in the basement and two things immediately rang alarm bells.
The first thing that hit me is that while the outgoing SWA is properly earthed to the box, the box itself is on a wooden backplate, and there is wood between it and trunking, and there is no supply earth at all. A measurement of 0.55 ohms between MET (2m away) and the box confirms this. (same measurement to trunking). I've had the trunking cover off and confirmed there is no connection of any kind at all. I haven't yet established where the 0.55ohms is coming from and might not do as other end of SWA is on the inaccessible roof.

[ElectriciansForums.net] Air circulation supply, no overload protection, no earth?![ElectriciansForums.net] Air circulation supply, no overload protection, no earth?!
[ElectriciansForums.net] Air circulation supply, no overload protection, no earth?!
[ElectriciansForums.net] Air circulation supply, no overload protection, no earth?!

That said it's easy to add an earth strap to the MET and remove that question.

2nd thing that hit me was that incoming 6mm supply is connected directly to the bus-bar chamber (160A fused 3 phase upstream main switch).
[ElectriciansForums.net] Air circulation supply, no overload protection, no earth?!

But as I'm well within 3m of the bus-bar chamber and it's run in metal trunking I'm thinking that though it feels and looks a bit strange 433.2.2 (ii) would in fact apply to this situation?
 
The Busbar layout is quite normal.
Every Chamber I worked on in over 50 years had multiple cables or copper bars of varying sizes.

The 0.55 maybe coming back through the steelwork the unit is bolted to on the roof or lightning conductor if the unit has one.
 
The Busbar layout is quite normal.
Every Chamber I worked on in over 50 years had multiple cables or copper bars of varying sizes.

The 0.55 maybe coming back through the steelwork the unit is bolted to on the roof or lightning conductor if the unit has one.
Thank you for responding. I guess I was mainly thinking that 160A main switch fuses wouldn't normally be sufficient OCPD for the 6mm supply to fused isolator.
So I was looking for a reason that it's 'ok' and double checking 433.2.2 (ii) was the answer, basically it's less than 3m and installed to provide minimal risks?
 

Reply to Air circulation supply, no overload protection, no earth?! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
295
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
277
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top