Hi Everyone,

I apologise, this is going to be a bit long winded! Any help would be gratefully received though.
I have just finished wiring the supplies for an air source heat pump. By manufacturers spec it needs a 32A supply outside for pump itself, and a 16A supply to the indoor control unit, so that is what I have given it. The existing installation is TT with a 10 way Hager CU and a separate 30mA 100A RCD/Main switch, the CU itself is old school with straight isolator (100A)

Basically the problem is that after installing the two circuits, and prior to connecting them I couldn't get a very good earth reading at the CU. I scratched my head for a bit, and then found that the connection to the earth rod had broken off, the earth rod by the way is only about 2 months old as they had had problems with nuisance tripping.....I dutifully reconnected the earth and continued (got a Ze reading of 232 ohms, a little high I know but given there was nothing before I was keen to carry on a worry about that at the end.)

Anyway, finished wiring everything and switched it all on, after about 5 mins the whole installation switches off at the RCD, and continues to do this randomly untill I switched off the PV to save it from damage. At this point the rest stayed on fine. At the moment the RCD seems happy with either the whole house and PV, or the whole house and Air source, but not both????

Is it possible to overload an RCD and will this make it trip? I am tempted to fit another separate two way CU for the Air source but of course there is very little room in there and the customer is beginning to look at me like a fool on the basis that "it was all OK before...."

Any tips would be very gratefully listened to. Thanks in advance, Ben.
 
Rcds don't protect for over current or over load......probably earth leakage current too high (more than 30ma or 100ma which ever installed), but saying that whoever put the p.v in they should have put t on its own little board with its own Rcd if applicable anyway, as they shouldn't share the Rcd with the house in a perfect world, so the customer may be able to get the p.v company back to change the arrangement they have got at the moment.
 
sounds like you've got both PV and heat pump on the same RCD, and the earth leakage current from both combined is tripping the RCD.

is this a whole house RCD ie 100 or 300mA RCD because it's a TT system or just the 30mA RCD for a split board?

if the latter, then you really want to be taking both the PV and heat pump off those circuits onto their own dedicated supply IMO - PV can cause nuisance tripping of RCD, and depending on the inverter can sometimes cause the RCD to stick, and the heat pump will probably have high start up currents, so may well need to be on a more industrial type MCB to allow for this - check manufacturers instructions and I'm sure it will tell you anyway.
 
Thank you both, having sat here reading for a bit I am beginning to see that generally PV is not installed on a shared RCD, let alone a 30mA one on a whole TT system, I did think this may be asking for trouble! Now of course I have the same old bother, go back to the customer and politely explain that although it is me that has just installed something it is still the PV installers fault...me thinks I might get a frosty response! Probably better for me to move the PV and see if it fixes it. Hey ho!

Thank you both again. Ben.
 
I wouldn't touch the p.v personally as its only started tripping once you've added the heat pump so just put that on its own Rcd board (garage board jobby) and everything should be honky dory, that's if you even need it on an Rcd
 
jdsparky, is that a little sarcasm directed at the PV installer??!!! You may be onto something because on the PV system there are no labels at all and the cable bringing it back to the CU is tw+e across the conservatory roof! I don't profess to be an expert but I do sometimes find myself looking at others work and thinking 'If you can't be bothered to do it right....'
 

Reply to Air source heat pump trouble...Help!!! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi Marconi, I have been trying to reply to your private message but am unable because of a Spam / content issue.
Replies
21
Views
4K
  • Question
Assuming the issue is because you want both to be switched via the same receiver you could always use a contactor to switch the load and use the...
Replies
8
Views
951
B
  • Article
Replace central heating gate valve with 2-port valve My house has a separate central heating loop that heats an annex. The annex loop has 3 x...
Replies
0
Views
227
Barnjet
B
We have just completed a self build, and heating system is Air Source Heat Pump, unvented HW cylinder, Buffet Tank, all Vaillant equipment. The...
Replies
0
Views
1K
Hello , I’m trying to further my knowledge into UFH/Rad/HW valves heating systems with air source pumps. What is normally needed outside with...
Replies
0
Views
752

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks