alarm going off when isolate light circut | on ElectriciansForums

Discuss alarm going off when isolate light circut in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Farmelectrics

-
Arms
Joined
Nov 9, 2010
Messages
3,057
Reaction score
520
Location
Wirral
just a quick one lads was changing a few lights for a friend when i isolated lighting circut the alarm went off obviously on same circut but this shouldnt happen isnt the battery ment to back it up had a look for battery none in hand set on wall i presume that its the one in the bell box thats gone i had no ladders to get up there would you say im right thoughts please
 
Hi there,
Yes you are correct the older alarms do this,the modern ones dont,you need to change
the alarm battery inside the alarm control box for it to work correctly.
Watch out for the boxes with keypads on as they have slim batterys.
 
sounds like you were looking in the keypad. the panel will be hidden away in a cupboard or even the attic. when you find it, measure the volts on the battery, with and without mains power. it could be an internal fuse in the panel.
 
Hold on new alarm or old alarm it makes no odds there are 2 rechareable batteries one in the panel and one in the outside sounder As for the panel battery this has a lifespan of 5 years (its always had a this even 30 years ago) after this period it will have a shorter lifespan so say it been in for 7 years then it may have 40 minutes of life in it instead of the standard 8 hours so a small power cut or dip and you dont see anything but after 40 minutes that or the battery no longer holds a charge then when the power is off the box outside activates independantly until this runs down .
How to fix it open the panel you will get a tamper fault remove battery and test the voltage on the leads so if you are getting say 13.5 vdc then fine get a new battery if not the panel may be damaged as it doubles up as a battery charger as well
 
generally, the battery life will be longer with the more expensive panels. some of the cheap mass market panels have charging circuits as rough as a bear's arse, and will reduce battery life.
 
its amazing how many people dont change batteries on intruder or fire alarms then expect them to work

Mogga its even more amazing that in the past the guys in the industry did not know either I said 30 years ago because thats when I got into alarms ie to give me an extra string to my bow due to Thatcher So rule No1 one is when fitting the battery write the date on the side and if you change it then do it every 5 years I have a 25 year old Optima 2+ panel in my house
 
generally, the battery life will be longer with the more expensive panels. some of the cheap mass market panels have charging circuits as rough as a bear's arse, and will reduce battery life. a quick check is t9 see if the battery is warm, and if the casing is bulging. then it's deffo. goosed. then measure thew volts on the batterey. should be 13.6v give or take. then dis. the battery. measure the charging volts and the battery volts. anything under 13.0v on either indicates a duff battery or panel fault.most panels have a battery fuse, and that can sometimes blow. generally it's 1.6A or thereabouts.
 
Mogga its even more amazing that in the past the guys in the industry did not know either I said 30 years ago because thats when I got into alarms ie to give me an extra string to my bow due to Thatcher So rule No1 one is when fitting the battery write the date on the side and if you change it then do it every 5 years I have a 25 year old Optima 2+ panel in my house
not with the original battery, i hope.:oops:
 

Reply to alarm going off when isolate light circut in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
885

Similar threads

Shhh, don't tell the Chinese they want a bit of the action.
Replies
1
Views
589
My experience with commercial lighting is when the fixture is ordered or bought the specs should say 120/277. Then their wiring diagram should be...
Replies
7
Views
567

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top