I need to fit an external sounder, but I need it to go off with either zone 1 or 2 ( mag 2 system) any ideas chaps
 
can you explain better as the sounder circuit would go off if either Z1 or Z2 in alarm, you also should have a volts free contact that would open or close in alarm this can be utilised for any external circuits but wouldn't be monitored so if your fittingg a extra sounder it should be incorperated within the monitored sounder cicuit to comply.
 
Right, so in an alarm state sounders go off on both zones, why is there two sounder circuits then ?, so for an external sounder I need to go out to that sounder from the board terminals and back again into the sounder circuit cable ends and connect in series or can I double up on the board terms but that would be a parralell connection which is not permitted according to the blurb with the alarm
Pict
 
Right, so in an alarm state sounders go off on both zones, why is there two sounder circuits then ?, so for an external sounder I need to go out to that sounder from the board terminals and back again into the sounder circuit cable ends and connect in series or can I double up on the board terms but that would be a parralell connection which is not permitted according to the blurb with the alarm
Pict


both sounder circs will go on alarm,just find the nearest sounder cable to where you want the external one and loop in and out,
 
Right, so in an alarm state sounders go off on both zones, why is there two sounder circuits then ?, so for an external sounder I need to go out to that sounder from the board terminals and back again into the sounder circuit cable ends and connect in series or can I double up on the board terms but that would be a parralell connection which is not permitted according to the blurb with the alarm
Pict
there are 2 alarm circuits as more a fail safe and its good design to overlap sounder circuit one with two in the areas to be covered so in the case of a fault blows the pcb fuse of on sounder circuit the other will still give good coverage, ive seen in past systems where a sounder circuit was wired to different floors but this should be now clear that its a poor design as losing one sounder circuit may not evacuate a floor in a fire but covering the floors with sounders balanced over the 2 alarm outputs and overlapping to a certain extent would still alert everyone.
 
Can only agree with DW's views on sounder circuit installation. 2 circuits are provided to try and lessen the issue of a single circuit failing for whatever reason under fire conditions, and areas of a building failing to realise there is infact a fire.

There should be a mixture of sounders of both circuits throughout all areas of the building rather than a single circuit confined to one area.

As for wiring, each circuit is treated as a radial circuit starting at the panel and ending at the final device of that circuit. Spurs & branches are not permitted.

The way to add devices (circuit permitting) is either (A) break into the radial circuit at an existing device and divert the circuit wiring to your new device, returning to the existing device using a suitable fireproof enclosure & connectors if neccessary etc. (B) Continuing on from the last device on the circuit to your new device, also you will need to move the EOL resistor from the previous last device to your new one. The last way which is often prohibited on some systems and seen as bad practice is to cut into the existing wiring and place a joint at this position, using suitable fireproof enclosures & accessories etc.

Any work you do should also be included on any existing fire alarm zone schedules or charts etc including any additional joints you have made.
 
Is the second sounder circuit possibly used for operating a relay which may inturn operate a phone modem/dialler?

Why have you asked this ian, an explanation for having 2 sounder circuits has been given by myself and Lenny and in comment to your post i wouldn't consider it good practice to spur of any sounder circuit to operate external unit like phone diallers as they would effectively be un-monited even if you looped into a relay to trigger a phone dialler i would still consider this bad practice, F/A panels have seperate alarm relays which are volt free just for this purpose or some more expensive panels have programmable outputs as well as pcb dialler card plug on options.
 
Just to add a bit of clarity, the sounder I propose to install will be out side, this is to alert the owners that the system has been triggered as they are a couple of hundres metres away in a seperate building and cannot here internal sounders, I can extend sounder circuit 1 from the downstairs bar area back outside via the beer cellar and the "new" sounder will become the EOL , thanks to all for making this a bit clearer for me
Pict
 

Reply to alarm sounder in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
969
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

D is the negative for the SAB hold off supply In the bell the 0v is linked to one side of the tamper switch and then the other side goes back to C...
Replies
3
Views
457
It's already the top spec model. Being a Dacia I think they were all fitted with a single tone horn. I'll have a look at what Amp rating some of...
Replies
5
Views
447

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top