Hi,

While doing an IR testing on the lighting circuits, these spot lights & transformers are a pain in the back side. The transformers are usually in the most inaccessible places and if you test them with 500v they get blown up or give undesirable results.

Is testing IR only between earth and live & neutral put together is acceptable in such situations?

Cheers!
 
As its a described method in GN3 then its acceptable.

If you can't disconnect them theres nothing else you can do, other than leaving the switch to them open, then you don't even test lives to earth then.

GN3 is worth its weight in gold mate.
 
It depends whether it's an initial verification or not.
If it is, then you should test before connecting any sensitive equipment.
If it isn't, then yes it would be acceptable to have such a limitation.
 
He doesn't know what it is
Here we go again!

Hi fuzzydunlop, every useless post is a waste of space on the server. Please stick around, read the posts at least twice, try to understand, ask questions if you are not sure and learn. Probably, one day you will have enough knowledge & confidence to help others on this forum.

Merry Christmas to you!
 

Reply to All these circuits with spot lights & transformers! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top