N

Noob2013

A friend has asked me to install a couple of extra sockets in there kitchen.

The consumer unit is an old Wylex with rewireable fuses so there is no RCD protection.

Would you carry out the work and recommend a new consumer unit/upfront RCD or would you not do the work unless they agree to have the extra work carried out aswell?

Some people are too tight or unable to afford the extra work so can't make them do it.

Cheers
 
obviously then a metalclad socket with SWA glanded in via a 20mm galv. coupler on the tiles of their ÂŁ10,000 designer kitchen.

Well it wasn't a ÂŁ10,000 designer kitchen, but a customer did ask me to change all their kitchen sockets for surface mounted metal clad ones. I also installed them a surface mount steel conduit lighting system with matching switch drops, completed with twisted cloth flex drops.
No shades installed on the brass lamp holders yet though. She is waiting to amass enough Victorian copper jelly moulds until she asks me to drill them out and mount them.

Not quite to my personal taste but the customer could not have been happier. I even got a bottle of wine and some cake when I went to drop off the invoice.
 
Talking of kitchens only last week I was in an empty recently purchased bungalow where the plumber was also the 'kitchen fitter'- the idiot had siliconed the hob down to a corian worktop which cost ÂŁ3k - before I'd connected the 4mm HO7 flex !! Just can't get to the terminal cover and connections on the back corner from below so he's gong to have to take the hob out, customer terrified that the worktop will be damaged but I'm not attempting it.
 
Talking of kitchens only last week I was in an empty recently purchased bungalow where the plumber was also the 'kitchen fitter'- the idiot had siliconed the hob down to a corian worktop which cost ÂŁ3k - before I'd connected the 4mm HO7 flex !! Just can't get to the terminal cover and connections on the back corner from below so he's gong to have to take the hob out, customer terrified that the worktop will be damaged but I'm not attempting it.

That is just stupidity personified .
How could anyone be so stupid.
 
That is just stupidity personified .
How could anyone be so stupid.

Yeah the muppet never seems to be around when I'm there, he also cut off the main water bond behind the sink so I had to chase out and get enough slack to fit a 10mm through crimp, and he told the customer that fitting the new shower to the wall in the shower room is my job even though he still has to put the existing pipe flush in the wall and it all has to be tiled yet, a real cretin ! :hammer:
 
Yeah the muppet never seems to be around when I'm there, he also cut off the main water bond behind the sink so I had to chase out and get enough slack to fit a 10mm through crimp, and he told the customer that fitting the new shower to the wall in the shower room is my job even though he still has to put the existing pipe flush in the wall and it all has to be tiled yet, a real cretin ! :hammer:

Fun to be had there then . Good luck with that one.
 
It's a nightmare, the poor woman regrets employing him but also tried blaming me for not connecting the hob 'in advance' - until I explained I couldn't until the worktop was actually 'on site'. :smile5:
 

Reply to Alterations on old rewireable consumer unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
794

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top