L
langstroth2
4kwp array. 20 degree pitch. Two Strings. Data below taken on a clear sunny day, the system is under load/generating. My problem is I can't work out whether the numbers are as expected / there's an array issue as comparing with a nearby array it seems to produce less power / or I just stop worrying!
Here's a screen shot from Sunny Design:
and here's the panel spec:
Pmax: 250W
Vmp: 49.08V
Imp: 5.09A
Voc: 60.36V
Isc: 5.56A
Eff: 14.7%
If I ignore VoC and ISC as I understand they are not relevant under load; and use Imp and PMax and Vmp. I also understand that these are figures under STC - and obviously this isn't "real world" - so I'd expect to see real numbers a % below.
So:
STC 1 string (panels in series) in theory is:
8*250W=2000W
8*49.08V=392V
5.09A
Where's as actual reading for string 1 is:
1696W (/250W=6.78 panels)
357V (/392=7.27 panels)
4.745A (7% drop)
This equals 7 panels. I am really "losing" a panel (and a bit) per string due to de-rating/pitch?
Pmax: 250W
Vmp: 49.08V
Imp: 5.09A
Voc: 60.36V
Isc: 5.56A
Eff: 14.7%
So:
8*250W=2000W
8*49.08V=392V
5.09A
4.745A (7% drop)