Sorry to ask such a fundamental question but this has been bothering me for a while now, I haven't come across an answer yet, and I want to make sure I get it right ...
For continuity of cpc, R1+R2 and polarity of domestic lighting circuits I was taught (at least this is what I wrote in my notes) to do the following:
1. Link the line & cpc of the circuit at the board
2. Check for continuity between line & cpc at ceiling roses - the test meter going beep is enough
3. Check for continuity between line and cpc at switches - again a beep is all we looked for
4. Measure the resistance between the switch return and cpc at ceiling roses to obtain R1+R2 for the circuit
Is this correct?
The reason I ask is that if I actually measure the resistance between line and cpc at switches I usually (if the cpc in the switch drop is smaller than the line conductor) get a slightly higher reading than the R1+R2 measurement I make at the ceiling rose. Also, for two way switching the resistance from each of strappers to the cpc at the switches depends on which switches are switched on and which are switch off.
So is it sufficient to just measure R1+R2 at a ceiling rose or should I be taking a measurement at the switch? Do I need to switch two-way/intermediate switches and repeat measurements or is any one of the ON switch combinations ok for R1+R2 measurements (it has little effect on measurements taken at the ceiling rose)?
Also, what do you do for ELV lighting where transformers and 3 plate connections are in the ceiling and can not be easily reached due to carpets and furniture, e.g. when testing following a consumer unit replacement?
Thanks in advance
For continuity of cpc, R1+R2 and polarity of domestic lighting circuits I was taught (at least this is what I wrote in my notes) to do the following:
1. Link the line & cpc of the circuit at the board
2. Check for continuity between line & cpc at ceiling roses - the test meter going beep is enough
3. Check for continuity between line and cpc at switches - again a beep is all we looked for
4. Measure the resistance between the switch return and cpc at ceiling roses to obtain R1+R2 for the circuit
Is this correct?
The reason I ask is that if I actually measure the resistance between line and cpc at switches I usually (if the cpc in the switch drop is smaller than the line conductor) get a slightly higher reading than the R1+R2 measurement I make at the ceiling rose. Also, for two way switching the resistance from each of strappers to the cpc at the switches depends on which switches are switched on and which are switch off.
So is it sufficient to just measure R1+R2 at a ceiling rose or should I be taking a measurement at the switch? Do I need to switch two-way/intermediate switches and repeat measurements or is any one of the ON switch combinations ok for R1+R2 measurements (it has little effect on measurements taken at the ceiling rose)?
Also, what do you do for ELV lighting where transformers and 3 plate connections are in the ceiling and can not be easily reached due to carpets and furniture, e.g. when testing following a consumer unit replacement?
Thanks in advance