Ok I get called to a job where there is no power to the flat. Intake is in a small basement cupboard, 25mm swa protected by a Bs88 80a fuse in a switch fuse. Test for continuity and the fuse has blown. Fit a new one and I'm sure you can guess the outcome..... New fuse blows.
Go up the the tenants cu and ir at 250v the incoming swa tails, live to neutral, live to earth etc and get a reading of around 150mohms on each. Now This job was last thing tonight and my brain is frazzled, what am I missing, the cu is a 16th edition skeleton board, around 15 years old, no one else is affected in the flats, oh and the new fuse blew with the main switch off
 
Do you make a habit of changing fuses without testing first... Id have been inclined to at least switch D.B. off and test the supply cable before replacing a blown fuse... then confirmed the circuits before energising if supply cable tested fine.

A bit arris about face your methods Pondy but I'm sure you'll do the correct sequence next time ;)
 
Since you tested after replacing the fuse and not before I would suggest that the fault has blown itself apart when the new fuse was put in.
It is always sensible to tests before replacing a blown fuse, especially when larger fuses are concerned.
 
On seeing a fuse of that size blown,more than a cursory glance would be necessary before jamming another round up the breach and shooting off in to the dark. :stooge_curly:
 
Agreed a spot of testing wouldn't of gone amiss, but I was parked in the road in a permit area and had one eye out for the traffic warden, the cu main switch was off darkwood,surely insolation resistance of the tails from the main switch back would of found an issue
 
The you should have parked more sensibly! What if the arc at the fault when you applied power had started a fire? Would you stand up in court and use your poor parking as an excuse for burning down a house?

Insulation resistance testing could have found a fault before you put the fuse in, but if the fault blew itself apart when the fuse was put in it won't now will it?
 
Adam, sorry yes I do mean mega ohms, dave sparks it wasn't poor parking and I wasn't making excuses, all the pay and display was full and there nearest was quarter of a mile away, and a permit space in the road outside the job was empty.
I don't understand quite what you mean, surely the fault is still there and as such should be traceable
 
I think what he's getting at is that with the power being put back on it's literally blown the fault clear. However what will be glaringly obvious now is something not working but with your main switch off it would point to a supply issue
 
You can blow a fault clear. But it’s usually due to damp. The heat of the flashover dries the fault out.

I spent nearly a month looking a UG cable fault. Every time the fuses blew it would test perfect afterwards. Finally found it by putting copper links in place of the 450A fuses. The ground erupted and a tree fell over, gave the game away really. The tree roots had disturbed a through joint and damp was getting in.
 
Adam, sorry yes I do mean mega ohms, dave sparks it wasn't poor parking and I wasn't making excuses, all the pay and display was full and there nearest was quarter of a mile away, and a permit space in the road outside the job was empty.
I don't understand quite what you mean, surely the fault is still there and as such should be traceable

For example if there was a short in an SWA cable where say a screw had penetrated it and made a connection between the armour and live then a large current will have flowed through the screw before the fuse operated. This fault current often manifests itself as a loud, bright discharge of energy which can dislodge the screw, melt through it or melt through the copper of the cable. Any of these things happening will remove the short circuit but obviously leave the cable significantly damaged.
 

Reply to Am I missing something here in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top