sythai

-
Arms
Joined
Apr 29, 2010
Messages
1,842
Reaction score
403
Location
Devon, United Kingdom
Shower / RCD problem... random tripping when shower is off (shower on it's own CU and RCD - Mira unit only a few months old)

Put my clamp meter on the CPC with shower running 80mA !! RCD not tripping though !! (not fully experienced with my clamp meter just yet only had it a couple of months)

Done a ramp test and trips at 25mA, x1 and x5 all well under

Disconnected tails from shower IR all clear >200.

Going to pick up another RCD to see how that is - crabtree starbreaker RCCB (sure I had problems with these before)

Any thoughts please ?

Thank you

Sy
 
Last edited:
Hi Sy, when using your leakage current clamp meter it's better to clamp round the Line and Neutral. Your meter will read the difference between the Line and Neutral currents (i.e. the leakage current), rather than the CPC. If the CPC is clamped you may measure any back feeding leakage from other circuits in addition to the shower final circuit leakage giving an apparently over large leakage current.
 
Last edited by a moderator:
Thanks Mark.... will try it that way didn't realise that could be done, couldn't believe it when 80mA showed up !

Oldtimer.... it's an 80a 30mA RCCB, just done the RCD checks with no load connected

[ElectriciansForums.net] Am I missing something obvious here...?
 

Reply to Am I missing something obvious here...? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
851

Similar threads

  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
3K
  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top