M
manda
Hi guys
Can you tell me if I'm getting this right, and if not can you see where I'm going wrong?
I have a dc circuit made up of: R1 6ohms and R2 14 ohms, connected in series,
R3 9ohms, R4 22ohms in parallel and also R5 6 ohms R6 6 ohms and R7 6 ohms also in parallel. The supply is 300v.
Total resistance I calculate as 18.8 ohms?
Total current I calculate 268.3 A
Voltage drop across R1 and R2 300v
Voltage drop across R3 and R4 0v
Voltage drop across R5 R6 and R7 0v
I get the feeling I'm totally off track though please can you advise?
cheers.---
I work out total resistance to be 28.4 ohms.
14 ohms & 6 ohms in series = 20 ohms
9 ohms & 22 ohms in parallel = 6.4 ohms
6 ohms, 6 ohms & 6 ohms in parallel = 2 ohms
If I read your description correctly you have
+300V --| R1 |---- | R2 | --- | Rp1 | ---- | Rp2 |--- 0V
Where Rp1 is R3 in parallel with R4
and Rp2 is R5 R6 R7 in parallel
R1 = 6ohm
R2 = 14 ohm
1/Rp1 = 1/9 + 1/22 SO 1/Rp1 = 0.1556 i.e. Rp1= 6.4
1/Rp2 = 1/6 + 1/6 + 1/6 SO 1/Rp2 = 3/6 i.e Rp2 = 2
Total Resistance between 300V and 0V = 6 + 14 +6.4 + 2 =28.4
This agrees with sintra so I guess he interprets the circuit the same as me
So I=V/R = 300/28.4 = 10.6A
Volt drop across resistors
V = IR
so
across R1 V=10.6 * 6 = 63.6V
across R2 V=10.6 * 14 = 148.4V
across (R1 and R2) = 212V
across Rp1 = 10.6 * 6.4 67.8V
across Rp2 = 10.6 * 2 = 21.2 V
Hopefully thats clear
Am I on the right track?
manda,
manda,