I am fully qualified and registered with napit, i am going to have some training on how to install fire alarm, but someone told me that only designated person can install fire alarm, other wise building control wont sign certificate for me, is it true or not? i know there are quite few certificates to be signed off, am i qualified to sign all of them or only some of them?


thanks in advance
 
I don't know of any regs that stop you installing but there may be some or insurance requirements that would prevent the design and commissioning element of the job

If you have no experience I would not recommend installing an addressable system until you have installed some conventional systems unless you can work with someone with experienced with addressables

Some good fire alarm info here Basic Guide to Fire Alarm Installation


If you want to check out how an addressable system is programmed it is worth downloading the XFP programming software from here C-TEC : Fire Alarms, Voice Alarms, Call Systems, Induction Loop Systems
 
Hi

any one can install fire alarm system

but at end of installation fire alarm system needs 2 certificates

commissioning certificate=which can be issued by rapproved Fire alarm company

Testing Certificate =which has to be issued by the maintenace company who is gona look after the system

Both certificates required by building control .
 
Hi

any one can install fire alarm system

but at end of installation fire alarm system needs 2 certificates

commissioning certificate=which can be issued by rapproved Fire alarm company

Testing Certificate =which has to be issued by the maintenace company who is gona look after the system

Both certificates required by building control .


How to be approved fire alarm company? can i get approved through the training course by NICEIC?
 
Hi
Been inthe fire alarm industry for last 10 years and I would agree with the advice to install first and get some one to commission the system. You will need however to supply a Installation Cert. Read BS5839 for install guide.
 
Hi again,
Sorry should have added try and obtain some formal training anyway its a mine field out there now. Not trying to be negitive just cautious.
 
Tks for the info have just been asked if I could fit a system for a friend! I have an easy answer - no!

Tks
Sparkles - the female Spark
 
I am qualified electrican with ELEcsa, domestic and commercial installer, what qualification do i need to design install and commision the fire alarm in commercial properties
 
There is no general qualification, but you do need to be competent.
The FIA do the best courses, but it is well over £1000 to do them all.
You'd really need a copy of BS5839 too if you are doing it regularly. That'll be another £150.
Then you need to check if your Insurance covers it, and you'll probably need to get Indemnity Insurance if you havent already got it.
 
IMHO, stay clear unless you are going to be doing plenty of installs and all the investment (as from above posts) will be recouped!
 
First thing before all the above.....You need correct insurance.....knowledge in Design, install and commissioning a fire alarm systems.
Ability to cad drawings for approval....ability to create final O & M, complete with as fitted......issue certification in Design, Install, Commission and Handover. When this can be achieved, start installing....before this can I suggest course in install and commissioning first, then after a few years move on to a design course. FIA will been you best starting point, on course training, and are the approved route to BAFE.
 
I have experience of installing in commercial property, went the cheeky route, get your friend to bring in CHUBB for a quote and produce a plan with costings, take approved plan to supplier for parts, install the alarm and then get a local firm to commission the install, save a wad of cash, know the system is approved and covered your a..e
 
I have experience of installing in commercial property, went the cheeky route, get your friend to bring in CHUBB for a quote and produce a plan with costings, take approved plan to supplier for parts, install the alarm and then get a local firm to commission the install, save a wad of cash, know the system is approved and covered your a..e
And the poor customer gets a closed system, with high cost maintenance each year, not really practical.....be better off linking up with a company you can partner with
 
I have experience of installing in commercial property, went the cheeky route, get your friend to bring in CHUBB for a quote and produce a plan with costings, take approved plan to supplier for parts, install the alarm and then get a local firm to commission the install, save a wad of cash, know the system is approved and covered your a..e

And the poor customer gets a closed system, with high cost maintenance each year, not really practical.....be better off linking up with a company you can partner with

Tazz I think he is just using chubb's drawings and spec to install a system and get it commissioned by others
 
chubbs drawings,spec and quote, supplier for approved parts, commissioned by a small local firm, who did set up an annual contract with me. Just saved on the chubbs horrendous labour costs.
 
Can see what your saying, but find it very hard to see Chubb would offer design drawings to a client, without clinching the job first.
At best you would get a list of materials with the quote....I certainly wouldn`t hand over cad drawings, and do all the design work for some one else to nick...
 
Thanks guy for the assistance, I now know that you need a little more thought into Fire Alarm Systems than originally thought.
 
First thing before all the above.....You need correct insurance.....knowledge in Design, install and commissioning a fire alarm systems.
Ability to cad drawings for approval....ability to create final O & M, complete with as fitted......issue certification in Design, Install, Commission and Handover. When this can be achieved, start installing....before this can I suggest course in install and commissioning first, then after a few years move on to a design course. FIA will been you best starting point, on course training, and are the approved route to BAFE.

Even our main contractor has subbed out the design, drawings, material take-off and commissioning to a specialised company. The only work the contractor will be conducting is the installation, and that will be ultimately supervised by myself. Fire alarm installations are not rocket science by any stretch of the imagination, it's the legalities involved that warrants specialised companies involvement...
 
Fire alarms are not rocket science.....but the design is precise and most sparks miss the maths used to complete a functional system.
If we take a smoke detector, with its detection range radius of 7.5 meters, and fit this into a square room, of 15m x 15m it will not actual cover the area, due to the being an a circular detection. So using an overlapping design, or a cross section measurement of 7.5m will give us a standard coverage of 10m x 10 m. There are many variations we use to design a system, height , area, envoiroment conditions and possible risks.
Its a shame really, that there are not many engineers entering the fire alarm industry, and as engineers retire, there is a big gap of cad/fire alarm designers
 
Last edited by a moderator:
Its a shame really, that there are not many engineers entering the fire alarm industry, and as engineers retire, there is a big gap of cad/fire alarm designers

I know I digress but "engineeers" entering industry/society in totality is a problem! In a society driven but material gains rather than vocational rewards, engineering is pretty far down the pecking order!
 
No its not rocket science,but unless the person has sufficient training,it can be a death sentence to the user

Yes it is pretty straight forward,running a few wires here and there and plonking some accessories and a panel on the cables

The design of fire alarm systems are best left to those that are trained and have the skill to ensure the system does what it is supposed to do,work effectively and within set parameters



I would suggest Get specialised fire alarm installation/commissioning and design trained or install the work designed and commisioned by someone who has had sufficient training
 
Also there is a small issue of something called "cause and effects" which are a mystery to most installers and engineers who poke their noses in to FA don't give it any consideration, and it is part of an engineers remit
 
Plant shutdown is a serious issue, along with lift grounding and disabled refuge communications......One which always gets me moaning is using class change for linking panels.
 
Dont know why High Tower, Xenex zones can be programmed for non latching, this allows the Xenex to show the addressable panel as a zone, and resets when the addressable is reset. The other good thing on gent Xenex, is the fire relays can be programmed to reset on silence.
 
Shopping centre, house alarm in a vig, each shop has a interface outside with a quad I/O, each shop had it's own xenex installed by us, 4 zone, all four zones in use (ground floor, first floor, stairs, sprinkler flow switch) so used a 4 core from each panel to interface, one pair signaling fire from the output on the xenex into one of the quad Chanel's as a input, then the other pair as a output back from the interface to the xenex class change as a output from the interface, there was also an addressable strobe next to each interface, sectored on the loop to activate when the shop panel it was above went off, 4 min delay on vig going into fire with key switch over rides on each shop panel.

Tbh only way I could think of doing it
 
Standard shopping center I/O setup....Not knocking too much, but is nice to see a zone show up for on the shops panel, indicating centers main panel, instead of just ringing bell with no indication.....Had a great cause & effect in a shopping center once....if shop panel activated, centers panel was delayed for 2 minutes then set off either side adjoining shops, but pulsed all others after a further 4 minutes, all pulsed shops converted to full alarm....was a long code to write
 
Standard shopping center I/O setup....Not knocking too much, but is nice to see a zone show up for on the shops panel, indicating centers main panel, instead of just ringing bell with no indication.....Had a great cause & effect in a shopping center once....if shop panel activated, centers panel was delayed for 2 minutes then set off either side adjoining shops, but pulsed all others after a further 4 minutes, all pulsed shops converted to full alarm....was a long code to write

i reckon i could just about manage that code, like you say, not rocket science but quite fiddly to configure.

Ill let you into a secret..........

There is a very well known shopping center group who shall remain nameless, for the purposes of this we will call them "Bestfield", they opened the country's biggest shopping center in 2012 adjacent to some stadium or something, all in time for some big sporting event.......vauge enough?? lol

The fire alarm contractor had only just become a Gent approved installer, and this was their first ever Gent job, possibly the biggest FA system i have ever worked on. 58 panels, 337 loops, 19,000 devices, all networked on domains.

The job was the undoing of this company and sent them under, they royalty cocked the cause and effects up!!!!, the biggest shopping center in the country, and the C&E were one out, all out!!!!! can you imaging the potential chaos!

I contact for the company that looks after it now, and they have an engineer there 5 days a week looking after the systems, i am the visiting contractor that looks after the place and i do all the alterations, installs and repairs.

When the center opened in time for this big sporting event, the system diddnt work and had no end of faults! it took 4 of us a MONTH!! to get the system working and to get the cause and effects right!
 
Fire alarms are not rocket science.....but the design is precise and most sparks miss the maths used to complete a functional system.
If we take a smoke detector, with its detection range radius of 7.5 meters, and fit this into a square room, of 15m x 15m it will not actual cover the area, due to the being an a circular detection. So using an overlapping design, or a cross section measurement of 7.5m will give us a standard coverage of 10m x 10 m. There are many variations we use to design a system, height , area, envoiroment conditions and possible risks.
Its a shame really, that there are not many engineers entering the fire alarm industry, and as engineers retire, there is a big gap of cad/fire alarm designers

Even with specialised companies being brought in for design and drawings etc, i've still had quite a few occasions where i've had to send the submittal packages back for corrections. Some of which have been quite bad discrepancies. So it's not always a case of these specialist companies always getting things right themselves...
 
Totall agree, find most of the local council designers to be the worst, missing roof voids, forgetting plant shutdown and always cocking db levels up.
This really should not be the case, fire design is set in stone, and a fire designer should have no excuse when working alongside building contractors
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
am i qualified to install fire alarm?
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
bluesky,
Last reply from
tazz,
Replies
34
Views
38,743

Advert

Back
Top