Hi All
Brother in law just moved into a council owned starter flat - small-ish with 1 bedroom.
The kitchen is on a separate ring main as are the lights and the outside lighting.
The socket circuit feeds ONLY 4 double outlets (2 in BR and 2 in LR) by looking at the CU it appears to be wired as a ring final with a feed out and feed return protected by a 32a RCBO using 2.5mm T+E.
Now I took off ALL the 4 face plates that make up the circuit and there is only 1 line 1 N and 1 CPC so it really appears that there must be a ring main to an unknown JB and tails supplying the socket outlets.
I have said to my Brother In Law that the 32a protective device is to big to be able to offer over current protection to the single tails, he called the council electrician to tell him my findings who visited the property today and said that yes there is a ring main under the floor and that the 32a protective device is OK.
As you would guess I'm saying to him this is incorrect and the council sparks is saying its OK - Who is right??
As you would imagine the council sparks has left in the 32a RCBO.
** there is no visible signs of fused spurs or accessible JBs that I can find**
**The cable run is run in part plastic trunk (grouped) then direct clipped to joists then in the wall up to the outlet**
I would be happy for a 16a protective device or a 20a max.
Brother in law just moved into a council owned starter flat - small-ish with 1 bedroom.
The kitchen is on a separate ring main as are the lights and the outside lighting.
The socket circuit feeds ONLY 4 double outlets (2 in BR and 2 in LR) by looking at the CU it appears to be wired as a ring final with a feed out and feed return protected by a 32a RCBO using 2.5mm T+E.
Now I took off ALL the 4 face plates that make up the circuit and there is only 1 line 1 N and 1 CPC so it really appears that there must be a ring main to an unknown JB and tails supplying the socket outlets.
I have said to my Brother In Law that the 32a protective device is to big to be able to offer over current protection to the single tails, he called the council electrician to tell him my findings who visited the property today and said that yes there is a ring main under the floor and that the 32a protective device is OK.
As you would guess I'm saying to him this is incorrect and the council sparks is saying its OK - Who is right??
As you would imagine the council sparks has left in the 32a RCBO.
** there is no visible signs of fused spurs or accessible JBs that I can find**
**The cable run is run in part plastic trunk (grouped) then direct clipped to joists then in the wall up to the outlet**
I would be happy for a 16a protective device or a 20a max.