Hi guys i calculating my expected maximum demand for an installation to see if the 60A cut out will handle it.
heres what will go in and calculations incl diversity
2X 32A Rings, so 32A(first ring) + 12.8A (40% all others)
1X 6A lighting, so 4A (66%)
1X10A lighting, so 7A
1X32A Shower, so 32A
1X45A cooker, 10A+ 40%of 35A= 24A
1X32A Under floor heating, 32A
so this equals 144A????
am i missing something this isnt right!!