No joy on the other thread, so I'll ask here:
I've got my AM2 in a week and I've been going over aspects of the assessment for the last few days so I hopefully don't make a silly mistake when the heat is on at the test centre.
I've been advised to just be calm and treat it as a normal install; i.e. if something is wrong, it isn't good enough. The main advice I've got is to just follow every aspect of the job spec that I will be given on the day, so obviously that is my plan. However, I haven't done much testing in the past and, as I still have a few days to prepare, I thought that I might as well ask the forum's contributors for some advice and pointers to help me out with a few things:
- Continuity: there is no box for R1 + RN on the testing form. Do I just make a note of it on the testing form, or is it not required in the AM2?
- On my insulation resistance test I plan to do a 'global' ten point test between all of the phases and earth from the mains switch. Obviously I have to remove all of the sensitive equipment, so I plan to put the light fitting's conductors, CO2 detector, RCD socket and the supply and load side of the motor into connectors and remove any neons. I also plan to switch off the spur on the S-plan heating system and I will then take the lowest readings I have for the global test and put them on the test form. However, I have been told to then connect the phase and neutral of the load side of the S-plan's spur and do an insulation resistance test through the heating system between those jointed cables and earth. This new value will be the S-plan's L-E insulation resistance value.
Will that be OK?
- I don't have any questions about Ze, PFC, and Zs (I plan to just summate this with my R1 + R2 values with Ze).
- Do I then do a phase rotation test? I'll be honest, I'm not sure how to do this. I remember once watching my boss do this test on a big chiller about a year ago and he just set the multitester to this function and put a three pronged lead on L1, L2 and L3. Is there a tester about that points in the right hand direction or something? How do I use this? Does this test come after all of the others I've mentioned as I can't see it listed in the On-Site Guide.
- RCD test and functional tests. Just remember to set the tester to 30mA and test both sides of sin wave at half, 1X, and 5X the tripping current. Do I record highest value here for each?
- Finally, I've heard different things from different people, but will I be required to check all my measured values comply with BS7671? If the answer is yes, I've found on the 'notes of schedule of test results' where to find these values in both the Regs and On-Site Guide.
How does all that sound? Have I missed anything required for the AM2? Never done fault finding before so that's gonna be a big stab-in-the-dark for me, so I'm just going to read as much as I can about faults in the next few days. The two-way lighting circuit is completely different to what I've always done in the past, but it seems pretty straight forward.
Any advice or help would be much appreciated. Cheers.