Hi guys,

Can somebody please help me out with the correct voltage drop on a 120mm 5core double insulated cable non armoured, on a 208v system , lay surface for a run of 10m. It has an ambient temp of 90 degrees / no thermal insulation and is being protected by 250A 3pole 60947-2 main sw.
I have worked out that the overcurrent protective device is oversized and requires reducing, but been a while since doing voltage drop calculations and nt 100% sure if i've got the correct voltage drop and want to confirm this. Could you please put down your figures ie Ca = 90 / Cg =0.6 etc so i can once again check mine.

Cheers
 
What regulations are you working to BS 7671 or the NEC ?

208 is 3 phase North America and the chances are you will be using AWG and their calculation for VD is done in imperial.
 
Its NEC installation but was working out to BS 7671, the cable is actually a 4/0 Awg but have converted into mm which equates to 120mm on the conversion chart given.
 
You need the AWG values of the cable I'm afraid, you can't work out a VD on that size of cable like your doing.

Also you will need to confirm what kind of load it is ie resistive, inductive or mixed.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ambient temps and voltage drop.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
sheeni,
Last reply from
sheeni,
Replies
4
Views
1,188

Advert

Back
Top