Quick question guys, if adding mains smoke alarms in a rental / domestic property's will we also need to provide SPD now. cheers all
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Amd2 SPD on smoke alarms in the UK Electrical Forum area at ElectriciansForums.net
A previous inspection I was picked up for not putting brown sleeving on the black interconnect wire on smoke alarms, even though all the NICEIC guides tell you to leave it unsleeved as it is an ELV control signal wire not mains switched live!If an inspector raises an issue, but can't give a reason for doing so (along with supporting evidence), I'd be inclined to think they were in the wrong job.
At the CEF 18th AM2 talk when mentioning SPD the guy said smoke alarms are not "safety systems" but as usual with no detail or justification for that point.
While there may be situations with a full CU where an overall SPD is not practical to fit for new alarms, in those cases you could just get the 10 year battery / wireless ones instead. If replacing existing alarm modules then you could argue it is not a new circuit so updated regs don't apply.
If it were a new hard-wired alarm I personally don't see how you could honestly say it is not for safety and so protection is optional.
Thank you for bringing this to my attention, I hadn't seen this before.As for old boards you'll probably find the Wylex REC2SPD (main switch and SPD in a self contained unit) used to afford type 2 protection of the installation. It could be argued that as it located "at source" that it should be a type 1 but you generally see those on LPS installations, See the BS EN 62305 series.
Fair observation, there may be others by other brands but the Wylex one immediately came to mind as we're familiar with the ubiquitous REC2 isolator.Mind you at ÂŁ122 + vat that's 2/3 of the cost of changing the board to a Fusebox SPD board with RCBO's anyway.
Crazy indeed, but AFAIK landlords can still install battery alarms, which is what they'll do if it's the cheaper option by a long way:Its getting crazy, as now all rentals need smoke detectors and to fit the new detectors (New circuit or alteration of lighting circuit) we need to install SPD, that's going to add ÂŁ100 + to the job just on materials. the clients/landlord are going to think we are taking the ----. as we know most landlords are tighter than a ducks .......,
That's good to know, but In Wales they got to be mains powered and interlinked.Crazy indeed, but AFAIK landlords can still install battery alarms, which is what they'll do if it's the cheaper option by a long way:
I feel this regulation needs rethinking, as it seems to be counter productive.
Probably a lot less work to fit the switch/SPD though than changing 5-10 circuits to get more board space (if no other pressing reason to change).EDIT Mind you at ÂŁ122 + vat that's 2/3 of the cost of changing the board to a Fusebox SPD board with RCBO's anyway.
With this being said about an spd must be fitted, after reading more and more into the set up and location of spds, an spd should be located less than 10meters from what ever it is protecting, with a type 2 spd located in a board and with a stand alone smoke alarm circuit leaving the DB the cable run is exceeding 10meters to multiple smoke alarms, does this mean type 3 spds will need to be installed at each smoke alarm to comply? Vert curious about this no more than 10meters rule as most electronic equipment will always be further than 10meters via a conductor from the fuseboard? Thoughts pleaseInteresting - was he saying that there were no circumstances in which their products could be used then, since they didn't until very recently make their own enclosures/MCBs?
Might be worth contacting Kirsty, their technical person, who is the one who told me that at an Elex a few years back. She is on some of the Regs committees I think, and might be able to provide something in writing to wave at any assessor in future....
I believe she was the one who always took the view that the main fuse was not an acceptable overcurrent protection and may have been partly responsible for companies like Hager changing their boards to include an MCB for SPD protection.
Although interestingly, in their guide they state that smoke alarms in a domestic property must be SPD protected, so I'd take that as fairly clear guidance from an industry source.
What is this 10m rule?
As you say, whatever device the SPD is protecting is surely more than 10m away.
Does it actually mean that, if fitting an SPD, it must be as close as possible to the circuit source OCPD? So inside the same CU, or in another enclosure very close to it.
I’m just wondering when the Scottish govt will come up with “ oh… you know all those smoke detectors we made you fit last year? We should have said, they need an SPD now. You’ll have to go back.”
At least they let us use the 10yr battery ones
Agreed but I believe this will be the way the regulations will go, time will tell, but either way its only going to get more expensive for customers and more overkill, will be the same with afdds they will be required for every circuit in the future.This is from an SPD manufacturer... not straight out of BS7671
They might have their own interpretation of how many are required for any given scenario.
But how effective is an SPD under all potential surge conditions and does a circuit need to be designed to mitigate the effects of any surgeThis is from an SPD manufacturer... not straight out of BS7671
They might have their own interpretation of how many are required for any given scenario.
Reply to Amd2 SPD on smoke alarms in the UK Electrical Forum area at ElectriciansForums.net