Amd2 SPD on smoke alarms | Page 2 | on ElectriciansForums

Discuss Amd2 SPD on smoke alarms in the UK Electrical Forum area at ElectriciansForums.net

Joined
Mar 20, 2013
Messages
34
Reaction score
4
Location
pembrokeshire
Quick question guys, if adding mains smoke alarms in a rental / domestic property's will we also need to provide SPD now. cheers all
 
If an inspector raises an issue, but can't give a reason for doing so (along with supporting evidence), I'd be inclined to think they were in the wrong job.
A previous inspection I was picked up for not putting brown sleeving on the black interconnect wire on smoke alarms, even though all the NICEIC guides tell you to leave it unsleeved as it is an ELV control signal wire not mains switched live!
 
At the CEF 18th AM2 talk when mentioning SPD the guy said smoke alarms are not "safety systems" but as usual with no detail or justification for that point.

While there may be situations with a full CU where an overall SPD is not practical to fit for new alarms, in those cases you could just get the 10 year battery / wireless ones instead. If replacing existing alarm modules then you could argue it is not a new circuit so updated regs don't apply.

If it were a new hard-wired alarm I personally don't see how you could honestly say it is not for safety and so protection is optional.
[ElectriciansForums.net] Amd2 SPD on smoke alarms

I would advise they actually read BS7671; verbatim from 18th Amd2
 
As for old boards you'll probably find the Wylex REC2SPD (main switch and SPD in a self contained unit) used to afford type 2 protection of the installation. It could be argued that as it located "at source" that it should be a type 1 but you generally see those on LPS installations, See the BS EN 62305 series.
Thank you for bringing this to my attention, I hadn't seen this before.
(In my view Type 1 would be overkill unless it was an overhead supply that is likely to be directly hit by lightening.)

EDIT Mind you at ÂŁ122 + vat that's 2/3 of the cost of changing the board to a Fusebox SPD board with RCBO's anyway.
 
Last edited:
Its getting crazy, as now all rentals need smoke detectors and to fit the new detectors (New circuit or alteration of lighting circuit) we need to install SPD, that's going to add ÂŁ100 + to the job just on materials. the clients/landlord are going to think we are taking the ----. as we know most landlords are tighter than a ducks .......,
 
Its getting crazy, as now all rentals need smoke detectors and to fit the new detectors (New circuit or alteration of lighting circuit) we need to install SPD, that's going to add ÂŁ100 + to the job just on materials. the clients/landlord are going to think we are taking the ----. as we know most landlords are tighter than a ducks .......,
Crazy indeed, but AFAIK landlords can still install battery alarms, which is what they'll do if it's the cheaper option by a long way:


I feel this regulation needs rethinking, as it seems to be counter productive.
 
Interesting - was he saying that there were no circumstances in which their products could be used then, since they didn't until very recently make their own enclosures/MCBs?

Might be worth contacting Kirsty, their technical person, who is the one who told me that at an Elex a few years back. She is on some of the Regs committees I think, and might be able to provide something in writing to wave at any assessor in future....

I believe she was the one who always took the view that the main fuse was not an acceptable overcurrent protection and may have been partly responsible for companies like Hager changing their boards to include an MCB for SPD protection.

Although interestingly, in their guide they state that smoke alarms in a domestic property must be SPD protected, so I'd take that as fairly clear guidance from an industry source.
With this being said about an spd must be fitted, after reading more and more into the set up and location of spds, an spd should be located less than 10meters from what ever it is protecting, with a type 2 spd located in a board and with a stand alone smoke alarm circuit leaving the DB the cable run is exceeding 10meters to multiple smoke alarms, does this mean type 3 spds will need to be installed at each smoke alarm to comply? Vert curious about this no more than 10meters rule as most electronic equipment will always be further than 10meters via a conductor from the fuseboard? Thoughts please
 
What is this 10m rule?

As you say, whatever device the SPD is protecting is surely more than 10m away.

Does it actually mean that, if fitting an SPD, it must be as close as possible to the circuit source OCPD? So inside the same CU, or in another enclosure very close to it.


I’m just wondering when the Scottish govt will come up with “ oh… you know all those smoke detectors we made you fit last year? We should have said, they need an SPD now. You’ll have to go back.”


At least they let us use the 10yr battery ones
 
What is this 10m rule?

As you say, whatever device the SPD is protecting is surely more than 10m away.

Does it actually mean that, if fitting an SPD, it must be as close as possible to the circuit source OCPD? So inside the same CU, or in another enclosure very close to it.


I’m just wondering when the Scottish govt will come up with “ oh… you know all those smoke detectors we made you fit last year? We should have said, they need an SPD now. You’ll have to go back.”


At least they let us use the 10yr battery ones
[ElectriciansForums.net] Amd2 SPD on smoke alarms
see picture I have attached, its abit unclear to me, when it says 10meteres from the electronic equipment I can only assume it is via actual cable length as this would be the path of the over voltage would take, like you say it would be garunteed all smoke alarm devices would exceed 10meters so this would warrant a type 3 spd to fitted at each smoke alarm device, this Is how I am interpreting this, some one correct me if I am wrong please
 
This is from an SPD manufacturer... not straight out of BS7671

They might have their own interpretation of how many are required for any given scenario.
Agreed but I believe this will be the way the regulations will go, time will tell, but either way its only going to get more expensive for customers and more overkill, will be the same with afdds they will be required for every circuit in the future.
 
This is from an SPD manufacturer... not straight out of BS7671

They might have their own interpretation of how many are required for any given scenario.
But how effective is an SPD under all potential surge conditions and does a circuit need to be designed to mitigate the effects of any surge

It is all very well mandating their use but IMO there needs to be more information put out regarding their use just because the regs say we must install them do we just go with what the manufacturer fits into it's CU's as the default device needed on a one type / size fits all or should we be giving more consideration to what devices we are fitting
 
BEAMA Guide to Surge Protection Devices (SPDs) – Selection, Application and Theory - https://www.beama.org.uk/resourceLibrary/beama-surge-protection-guide-.html for download.
Although not out of BS7671 we still need to install it according to the manufacturer's specifications.
I think we should be looking more into what devices we need to fit, as UNG has suggested.

Schneider reference:-
SPD Type - used to describe the intended application location of the SPD, either upstream or downstream of the main overcurrent protective device of the facility. SPD Types include:

  • Type 1- A permanently connected SPD intended for installation between the secondary of the service transformer and the line side of the service equipment overcurrent device, as well as the load side, including watt-hour meter socket enclosures and Molded Case SPDs intended to be installed without an external overcurrent protective device.
  • Type 2- A permanently connected SPD intended for installation on the load side of the service equipment overcurrent device, including SPDs located at the branch panel and Molded Case SPDs.
  • Type 3- Point of utilization SPDs, installed at a minimum conductor length of 10 meters (30 feet) from the electrical service panel to the point of utilization, for example, cord connected, direct plug-in, receptacle type SPDs installed at the utilization equipment being protected. The distance (10 meters) is exclusive of the conductors provided with or used to attach SPDs.
  • Type 4- Component Assemblies -, a Component assembly consisting of one or more Type 5 components together with a disconnect (internal or external) or a means of complying with the limited current tests.
  • Type 1, 2, 3 Component Assemblies - Consists of a Type 4 component assembly with internal or external short circuit protection.
  • Type 5 - Discrete component surge suppressors, such as MOVs that may be mounted on a PWB, connected by its leads or provided within an enclosure with mounting means and wiring terminations.
 

Reply to Amd2 SPD on smoke alarms in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
456
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Thank you all, yes I didn’t think they do and I have done minor works but the helpline was not very helpful. Got my yearly assessment soon so I...
Replies
4
Views
326
What makes it a lack of space? I’d say to the customer to dismantle a cupboard or whatever to creat the space you need for the extra equipment...
Replies
1
Views
235

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top