Joined
Apr 23, 2019
Messages
256
Reaction score
272
Location
south west
So I need to add a new circuit, I was going to do it to amendment 2.. Its a commercial property and will be adding a new circuit for a defibrillator cabinet and associated accessories (lights)... There is a decent enough 3 phase board in place, but there is no SPD.. Obviously if we add a new say socket circuit it has to have RCD protection even if there is no RCD protection in the existing board, this could require a new board. With SPD's now being mandatory (Apart from if customer refuses) what are peoples opinions.. There is no room to add an SPD in this three phase board so to add an SPD it would require a completely new board which would cost thousands and its out of the question...

The transformer is only a few houses away and all cables are underground and in the 60+ years the property has been there they have never had an issue with a transient voltage..

Is it ok to add a new circuit under amendment 2 without an SPD? (I am leaning towards yeah just add the circuit, having to add an SPD to an existing installation when it is not easily done is ridiculous)
 
Just note on the eic, recommend spd is insatlled customer currently does not want costs involved.

Yeah I think thats a good shout, my thinking was adding a new circuit for a few hundred quid to a defibrillator enclosure which the actual enclosure is worth not that much with just a small heater and light in it is not really going to make it any worse... But highlighted to me the problem as 99% of installations will not have an SPD... I guess the argument is you don't change a plastic board to metal to add a new circuit so why would you install an SPD, would you note a plastic consumer unit? I guess its not a big change from the last amendment and I installed new circuits without adding SPD's.. Obviously if I was changing the consumer unit then I would add an SPD but I guess common sense has to kick in at some point..
 
As @loz2754 says there are a few external box solutions for existing TPN boards. Usually the catch is you need a spare way to connect it to the busbars, either by "neutral links" as Hager offer, or using something like a 50A D-curve MCB for low inductance, or I think fuses (obviously) in the case of Ryefield board add-ons.

The cables to the SPD need to be short for low inductance, ideally no more than 0.25m (so loop is 0.5m max, though you can go to 0.5m for 1m loop but keep cables tight together for low loop area) so usually the box has to be mounted on the side of the existing DB.
 
So I need to add a new circuit, I was going to do it to amendment 2.. Its a commercial property and will be adding a new circuit for a defibrillator cabinet and associated accessories (lights)... There is a decent enough 3 phase board in place, but there is no SPD.. Obviously if we add a new say socket circuit it has to have RCD protection even if there is no RCD protection in the existing board, this could require a new board. With SPD's now being mandatory (Apart from if customer refuses) what are peoples opinions.. There is no room to add an SPD in this three phase board so to add an SPD it would require a completely new board which would cost thousands and its out of the question...

The transformer is only a few houses away and all cables are underground and in the 60+ years the property has been there they have never had an issue with a transient voltage..

Is it ok to add a new circuit under amendment 2 without an SPD? (I am leaning towards yeah just add the circuit, having to add an SPD to an existing installation when it is not easily done is ridiculous)
How's about a single phase sub board with its own type 2 SPD close to the protected equipment , < ÂŁ100 populated
 
How's about a single phase sub board with its own type 2 SPD close to the protected equipment , < ÂŁ100 populated

That would comply, but its protecting a defibrillator cabinet, which is a small light and a heater, which would be less value than the ÂŁ100.. There is also limited room to put an extra board... I think the easiest way is to just offer to replace the consumer unit or they can sign to say they dont want an SPD...

But it does raise a problem, where do you stop..
Do you have to install an SPD if doing maintenance work?
Do you have to install an SPD when adding to or altering an existing circuit?
Do you have to install an SPD when adding a new circuit?

Most customers may have room for a new circuit or two but not an SPD and new circuit, so are we to rip out new consumer units that are less than a year old? I understand they have made it simpler and its to stop the cowboys that were changing consumer units without fitting an SPD saying it wasnt needed... But by being so rigid they have caused a massive headache..
 
Last edited:
Most customers may have room for a new circuit or two but not an SPD and new circuit, so are we to rip out new consumer units that are less than a year old?
Well if less than a year old it ought to have had SPD already!

You can get single module width SPD but usually they need some back-up MCB so no real space-saving over the double-width ones that are OK with the DNO's 100A max fuse. So yes, fitting a new circuit and SPD typically means 3 spare slots in the CU being used up.

Or its the external module, maybe some conduit coupler between enclosures so singles can be used between them and earth to chassis. Not ideal but off the shelf like:
 
But it does raise a problem, where do you stop..
Do you have to install an SPD if doing maintenance work?
Do you have to install an SPD when adding to or altering an existing circuit?
Do you have to install an SPD when adding a new circuit?
My usual pragmatic test is if doing an EICR afterwards would the change be worse than a C3.
But If installing a new circuit that circuit will comply with amendment 2.

For example - you get asked to add an outside light in a care home, and it has a Hager dual rcd board (type A for arguments sake). The lighting breakers are already 'busy' but there's a spare way. Do you:
a) add yet another branch to one of the lighting circuits
b) add a B6 to the spare way
c) say sorry you need a new metal CU with SPD and AFDDs, quote to fit outside light is ÂŁ1200
 
One reason here that SPD seems important here is this is for a defibrillator - you could argue that if it is damaged by a surge then it has direct implications for saving someone's life should it be needed.

But it could be local to the install via a small DIN rail box so power feed goes through this to SPD for low inductance (as no real loop of cable) or it could be adjacent to the main CU and linked via D-curve MCB or similar to protect all of the install.
 
Last edited:

Reply to Amendment 2 new circuit SPD? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
You'd have to be mindful of SPD conductor lengths doing it that way. I think Matt:E make a single board with Type A RCBO, openPEN detection and...
Replies
1
Views
1K
  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top