Hi All,

Having done my model for Amtech LV. I have noted that when Descriminating between two breakers the Pscc is taken at the load end of the circuit when analyazing discrimination between breakers.

Example being:-

The discrimination limit between upstream device Q1 and downstream device Q2 is 1.25kA. the fault current at Q2 is 10kA, the fault current at the load end of the circuit downstream of Q2 is 1kA. Amtech is telling me that I am achieving discrimination as Pscc is below 1.25kA. When I play around with circuit lengths, I managed to get a fault current of 1.5kA at the end of the circuit being supplied from Q2, only then did the program come with a warning for discrimination.

[FONT=Arial, Helvetica, sans-serif]Any ideas? I thought it is unusual that Pscc is taken at the load end of the of circuit. Shouldn't it be taken at the maximum (source of the circuit?) Are there different ways in interpreting BS Standards that I am not aware off? [/FONT]

Many Thanks
 

Reply to Amtech and Fault Current and Discrimination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
447
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
981

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top