AndrewB

Morning Gents,
I hope that you can help me with this problem. I am not an electrician - I just know enough to be dangerous.

I recently bought this beautiful beast :

[ElectriciansForums.net] Ancient single phase electric motor  - reversing the rotation

It's a Denford tools Viceroy pillar drill from the 60s or maybe even the 50s. Nice and cheap with one catch - it had a non original 3 phase motor with some strange rating on the data plate which baffled both the bloke I bought it from and my friendly electrical expert. Therefore - much as I would have liked speed control - I went the easy route and bought an ancient AEI single phase motor with the necessary – and hard to find - 5/16” shaft for a tenner.

[ElectriciansForums.net] Ancient single phase electric motor  - reversing the rotation [ElectriciansForums.net] Ancient single phase electric motor  - reversing the rotation


Having played with the internal shimming, fabbed up a new bracket and swapped the contactor I now have a lovely working quality pillar drill for under ÂŁ80. I like a bargain.

However - it goes the wrong bloody way round and as I want to make holes not fill them I'm a bit puzzled.
I swapped the L and N on the motor - no difference. A quick google tells me it must be a split phase motor - never heard of them.

So chaps - what do I (can I ?) do ?

An idler pulley is an option but a lot of faff. I can't afford any more major expense on another motor or going the 3 phase route - I want to work with what I've got.

If I open up the motor (been in there already for a once over and to free it off) can I swap the orientation of the central outer section (don't know the correct term) whilst leaving the armature and end caps in the same relative positions. I'm guessing there will be a couple of wires to swap as well although as the photo shows - the 2 supply cables are connected to the centre 'barrel' NOT the bottom end cap.

Logically - when these motors were built - they must have been designed so that they could be provided with either rotation so as to suit different applications ?

I'm sure it's not quite that simple but any advice would be appreciated.

Cheers

Andrew
 
Last edited by a moderator:
Nope - no capacitors externally and didn't notice any inside but then I wasn't particularly looking.

As I understand it - which isn't a lot - a split phase doesn't have capacitors.
 
As an eBay Associate we earn from qualifying purchases.
This is the non original 3 phase motor that was on it - which the previous owner hadn't manged to understand or get working.

[ElectriciansForums.net] Ancient single phase electric motor  - reversing the rotation

He and others told me that fitting an inverter is not an option with this motor. Can't remember if it was the STAR configuration or the 400/440 in the voltage box (i.e. NO mention of 240) that was thought to be the problem.
 
Last edited by a moderator:
You should be able to use inverter start on a Star motor to be honest. The inverter supercedes the need for star/delta start on a 3 phase motor

I'm no motor expert by any means and some of the more knowledgable lads may shoot me down, but what Sean posted would seem to work for me, and well what have you to loose?

Edited because I put delta instead of star
 
Last edited:
I'm no expert either but isnt star wired the same as Y - most of my old 3ph machinery is either star or Y plated, and I've connected them up the same.

Can you post a picture of the windings terminations ?
 
That old 3 phase motor doesn't have an insulation class high enough to be run on a VSD.

That being said, it could run fine for years on a vsd...

400 volt output in star will likely mean it needs 230V delta. Leave it wired in star, the vsd will come as default with a 400v output.
 
The motor is Flp (flameproof) and in the terminal box there is no access to the start winding.
To reverse this motor the start windings need to be swapped. the start winding is usually thinner and is connected to a simple centrifugal switch. The motor will have to be stripped down to access the windings.

[ElectriciansForums.net] Ancient single phase electric motor  - reversing the rotation

In the above drawing i have not connected the start windings to anything just tried to explain where they need to go

Found this on youtube it shows inside the motor and the centrifugal switch can be seen

https://www.youtube.com/watch?v=Mnz82o1XYeg
 
Last edited by a moderator:
Not seen a vsd that is 230v single phase input and is 400v 3 phase output There may be one but its not common and suspect a heavty price tag.
most vsds output the voltage they are inputted with they just change the phase and frequency
 
Not seen a vsd that is 230v single phase input and is 400v 3 phase output There may be one but its not common and suspect a heavty price tag.
most vsds output the voltage they are inputted with they just change the phase and frequency

VSDs with a 230V input are common as muck, and aren't a lot more money.

Just had a look, entry level 230V VSD's are cheaper.

http://www.parmley-graham.co.uk/var...e-phase/sinamics-v20-entry/6sl3210-5bb15-5av0

Obviously Siemens is one of the top end brands so cheaper will be available.
 
Last edited by a moderator:
VSDs with a 230V input are common as muck, and aren't a lot more money.

Just had a look, entry level 230V VSD's are cheaper.

6SL32105BB155AV0 / 6SL3210-5BB15-5AV0 - Siemens V20 - 0.55 kW / 3.2 A (FSA without fan), Filtered

Obviously Siemens is one of the top end brands so cheaper will be available.

All correct Rob But the output on a 230v VSD is ???? and the motor is wired in star at 400v it will run but at a fraction of its power because of the reduced voltage
please check the output voltage of the VSDs 230 in =230 out 400v in =400v out

Cheers Myke
 
I'm with Rob, high dv/dt issues associated with VFD's will destroy the windings of an old motor, you can add filters but rather don't go there, it can get quite involved.

If it is a split phase motor there's two ways to reverse the direction, either you can reverse the two wires of the start winding or you can reverse the run winding. Actually there's three ways, you can also occasionally unbolt the two end caps of the motor and reverse the entire stator but this is not advisable unless you know the motor was specifically designed to do this.

To reverse the start winding you'll probably have to remove the entire termination block with the connection posts on it and look underneath it. You should see the four winding wire connections under there. To identify the start winding you'll need to resistance test both windings and the start will be the one with higher resistance.
 
All correct Rob But the output on a 230v VSD is ???? and the motor is wired in star at 400v it will run but at a fraction of its power because of the reduced voltage
please check the output voltage of the VSDs 230 in =230 out 400v in =400v out

Cheers Myke

Output can be set to 400v with a 230v input
 

Reply to Ancient single phase electric motor - reversing the rotation in the Electrical Tools and Products area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

On a small generator I wouldn't want to risk using diversity as they are not quite as forgiving as a mains supply and can very quickly fail when...
Replies
8
Views
703

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top