And another mad question ("minimum current") | on ElectriciansForums
Discuss And another mad question ("minimum current") in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Lincolnshire
28. Which one of the following is not considered when calculating the minimum current carrying capacity of live
conductors of a cable?
a Ambient temperature.
b Grouping.
c Type of protective device.
d The maximum permitted volt drop.
Good stuff find device rating divide by factors, look up increased calculated current against correct table and check install method column choose nearest highest value. Then worry about volt drop
The way I read the question is you would select the cable on the size of protective device so it would have a bearing on it. Ib<In<Iz
So with a 20A radial, what effect would the 20A protective device have on the CCC of the cable used to wire the circuit?
Better still, consider designing a cooker or a shower circuit.
What is the first thing you need to know?
But ask yourself why do you put the 20A MCB on that radial??
First you need to know the total design current for the circuit. For arguments sake say 7A of lights on a radial. You would then choose your protective device based on this calculation. So say you choose a 10A 60898MCB, forgetting derating factors for now you would then choose a cable with a current carrying capacity higher than the protective device chosen.
The only thing not needed in the OP question for CCC calcs is VD
You take a protective device of current rating C, the minimum current carrying capacity of a live conductor connected to this protective device is C (or 0.725C for semi enclosed fuses), however the cable is grouped with other cables so limiting the current that can be taken on the live conductors so now the minimum CCC is C/cg, but the cable is in a high ambient temperature so the minimum CCC of the cable is now C/cg*ca.
The minimum to which the current carrying capacity of the cable can be taken is C/cg*ca therefore you have calculated the minimum CCC of the live conductors by taking into account the type of protective device, the ambient temperature and the grouping.
The volt drop does not enter into the CCC calculation, it may be very relevant for compliance but not for current carrying capacity.
Reply to And another mad question ("minimum current") in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
nicebutdim
N