regarding volts drop

i have an equation of

mv x ib x l / 1000

so what is the equation

(r1 + rn) x cf x ib
answer x 100 / 230

will somebody please clear this up
 
Voltage = Current x Resistance (V = I x R)

r1 + rn is the resistance of your circuit at 20°C.

cf is the correction factor for conductor operating temperature. As resistance increases with temperature you need to adjust it for 70°C. You do this by multiplying your measured resistance by 1.2

You then multiply the new value by your design current which gives you the voltage drop on the circuit at 70°C.
 
Upvote 0
Both. It's up to you. They will both give you the same result.

The mV/A/m values from your first equation are calculated using the other equation.

mV/A/m = (r"1 + r"n) x 1.2 where r"1 = resistance per meter of line conductor and r"n = resistance per meter of neutral conductor.

So in the case of 2.5mm² you would get...

r"1 = 7.41mΩ per meter
r"n = 7.41mΩ per meter
r"1 + r"n = 14.82mΩ per meter
(r"1 + r"n) x 1.2 = 17.78 mΩ per meter (rounded up to 18) which is the value in BS 7671
 
Upvote 0

Reply to another 2391 question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
414
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
As you have actually measured the cold resistance (R1 + Rn = 0.15) then you have the voltage drop at the expected current (60A) so you can compute...
Replies
2
Views
1K
Hi Mike, Floating Neutral. I'm really over simplifying below, but using generators as an analogy is possibly easier to understand. In a large 3...
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top