A

ABerry82

i have been asked to install a garage unit in a outbuilding they wanted a couple of sockets and lights and i think i allowed about 20A total output for design current. what size cable do you think bearing in mind its a 90 meter run in a trench from house to out building.i allowed 16mm does this sound like overkill
 
Are you suggesting 16mm on a rule of thumb or have you calculated it taking vd into account? It may seem overkill but a 5% or 11.5 volt drop on a 230v single phase supply from supply cutout to your outbuilding will require an apparently large cable. I would normally design a sub-main vd calc on 2.5 to 3% so you can have allowance of around the same on your final circuits. Enjoy!
 
What type of "Garage"? If its one you park cars in then fair enough, but the 90M walk to the house in a winters nights is a bit of a nightmare. In fact a nightmare at most times. 20Amp probably enough there, its not like they will be putting tumble dryers or washing machines in it that far from the house.

If it's a garage to work on cars/projects etc then 20Amp may be shy, could be the likes of a welder going in. I'd visit site, get a proper spec of what is going to be used out there and a proper distance from the house. Customer estimates on distances and the like tend to be well off and there is no point in wasting your own time sizing and pricing up cable until you know what you need.
 
why have you allowed 20A?.....assume your going to use a 16A MCB...for the outlets....and a 6A MCB for the lighting......thats 22A mate.....
but that's the MCB ratings, not the design current. would need a lot of lights to pull 6A.
 

Reply to Another cable sizing question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
184
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
560
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

  • Question
Issue is certain sizes of cable may theoretically be okay but upon the proper testing when it’s commissioned things like a thing may not test out...
Replies
8
Views
1K
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top