Hi guys I need to find the installation method for a twin and earth cable run in a stud wall touching the wall in insulation for 13meters, I've referred to the regs and I have come up with install method 102 does this sound right to anyone ( page 67 OSG)
 
Have a look at table 4A2, near the end there are the installation methods for twin and earth when covered with insulation, these then refer you to the appropriate current carrying capacity table.

102 is correct.
(what is on page 67 of the OSG?)
 
hi Richard sorry to bother you again, i also have to find out the tabulated current, so using the factors of Ci - 0.51 and Ca - 0.94 i done the following of 20 divided by (0.94 x 0.51) which gave me 41.71 amps, then when i went to page 340 table 4d5, column 4 it says i need a CSA of 10mm2, is this correct as it seems very big to me or have i gone wrong somewhere?? its for a 4kw storage heater.
 
Last edited by a moderator:
( 4kW is 16.6667A, so 4 mm gives 32A so that would be my choice.
 
Last edited:
Yes if your cable is surrounded in insulation for those 13 metres then you use a derating value 0.5 for 500mm or more. So in affect you are halving the current carrying capacity of the cable
 
16.6667A is 4000 divided by 240, i divided by 230v, on the paper it doesnt state 230 or 240v, not sure which one to use now,
 
cheers guys it makes sense now i m just happy im going down the right route, thanks again
 
Reference method 102, Ambient temperature 30°C and Conductor operating temperature 70°C the current carrying capacity of 2.5 T&E is 21 amps. Your 4kw heater is going to pull 17.39amps.
 
Remember that reference method 102 tabulated current carrying capacity has already factored in the Ci correction factor so you do not need to do this again.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Another college query
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
11

Thread Tags

Advert

Thread statistics

Created
davedwr1978,
Last reply from
Richard Burns,
Replies
11
Views
135

Advert

Back
Top