Went to look at a job today and came across a recently replaced consumer unit fed by 6mm tails protected by 100 amp supply fuse consumer unit was a 10 way dual rcd supplying a 9.5kw shower, cooker, immersion heater, ring main and two lighting circuits surprisingly no label on cu and no certification and to top it all no bonding to water main. was probably done by kitchen fitter as new kitchen fitted bout the same time
 
I was asked the other day to go with my builder mate to look at an installation at a house he's been asked to work on & offer my advice.

The house was an unoccupied 2 bed terrace with the leccy supply via a pole in the street, and it's a TT. Inside the house high up on the wall in the hallway we have the cutout & supplier's fuse, 16mm tails from that to the meter & again from meter to a stand-alone 60A 30mA RCD, then 16mm tails from there to a Wylex board fitted with those plug-in MCBs.

The first thing I noticed was all the CPCs connected to the Earth Bar in the CU, but no Green/Yellow cable coming from it to an Earth Stake, Gas Meter or Water Stop Cock. No signs anywhere of a MET either, so there is no "proper" means of earthing or bonding anywhere on this installation.

We wandered into the kitchen & the first thing we saw was a relatively new Baxi Combi boiler and I am forced to conclude that the tap rail of this boiler must be the only means of bonding the gas to the water, and offering a bit of an earth through the water & gas pipes.

Next, we looked at the built-under electric oven which was connected via plug top to a socket in an adjacent cupboard, and then we looked at the electric hob - 8.4kW hard wired all the way back to the CU by means of a length of 2.5 T&E which was draped down the back of the oven, then laid on top of the central heating pipes along the skirting, then up through the ceiling along with the central heating pipes & boxed in with them. It then somehow ran under the floor of the bedrooms until it emerged from the ceiling in the hall & entered the CU where it was "protected" by a 32A plug-in MCB.

While investigating in the kitchen, I came across a bit of paper bearing the British Gas logo / letterhead etc. in a drawer next to the cooker, & on reading it, found it to be a report on the electrical installation stating that there is no bond on the gas meter and the Earth Fault Loop Impedance is more than 200 Ohms. (not surprising really) and this paper was dated November 2010 !!!! So, here we are two years later and still these issues have not been addressed !!!

My builder mate asked me what it all meant & I explained it to him in very simple terms that basically it was a very unsatisfactory condition to say the least. He then phoned the property owner - an absentee landlord - and told him what we thought. His reply was "Well it's been working all this time with no problems ......"

Meanwhile - while all this has been going on - our other mate who is a gas fitter was removing the gas fire in the lounge because it was in a dangerous condition !!!

So there we have it ... the landlord is happy to accept and act upon the findings & advice of the gas fitter, but not those of the electrician !!! :banghead:
 

Reply to Another cowboy in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top