So changed a CU and doing CPC check,
1. a circuit going to an aerial booster in the loft had been crimped and taped together instead of jnc box(in the loft), so couldn't gain access to cpc without dismantling the 'connections'.
Should i undo the connections to do the CPC test or just list on schedule of test results that couldn't access terminals of circuit to test? ( i dont want to take responsibility of this circuit by dismantling it)
2. The built in cooker couldnt be removed so i tested at the cooker switch and noted that the test was to cooker switch only! this ok?
3. Their was a circuit going to the bathtub SPA bubbly thing, again i couldn't gain access to the termination of the circuit as it was sealed under the bath. i noted i couldn't complete CPC or Zs test on schedule of test results.
4. also, the tails from the supply cut out run for about 1meter, 2mm below the plaster and not in safe zones, what you advise i should do about this? - Note it?, advise customer/DNO? i dont see another way of getting tails to cu other than surface mounting them.
What would you recommend guys??
thanks
V
1. a circuit going to an aerial booster in the loft had been crimped and taped together instead of jnc box(in the loft), so couldn't gain access to cpc without dismantling the 'connections'.
Should i undo the connections to do the CPC test or just list on schedule of test results that couldn't access terminals of circuit to test? ( i dont want to take responsibility of this circuit by dismantling it)
2. The built in cooker couldnt be removed so i tested at the cooker switch and noted that the test was to cooker switch only! this ok?
3. Their was a circuit going to the bathtub SPA bubbly thing, again i couldn't gain access to the termination of the circuit as it was sealed under the bath. i noted i couldn't complete CPC or Zs test on schedule of test results.
4. also, the tails from the supply cut out run for about 1meter, 2mm below the plaster and not in safe zones, what you advise i should do about this? - Note it?, advise customer/DNO? i dont see another way of getting tails to cu other than surface mounting them.
What would you recommend guys??