Be warned it you are tempted by shortuts. I know in domestic work on old houses, we often have a race against the clock, and it can get stressful and sometimes very difficult, but some cut corners could bite.
I have just fixed errors left behind by NIC member who fitted new 17th ed'n consumer unit a couple of years ago. TN-S install.
Table of results taped neatly next to CU, all the labels in place, looks good.
It turns out that lighting R1+R2 were fabricated, presumably from Zs-Ze.
Half the house lighting had open circuit CPC, neatly hidden by a perfect N-E short on the far side of the break. "Zs" values throughout all the fittings were believable, (but not really Zs anyway since no CPC). Very obvious with proper R1+R2, or even with NE IR test done at at far end. (All IR of course was good at consumer unit)
The error included all the lighting throughout a large flat roof extension and bathroom. All class1 light fittings.
I have just fixed errors left behind by NIC member who fitted new 17th ed'n consumer unit a couple of years ago. TN-S install.
Table of results taped neatly next to CU, all the labels in place, looks good.
It turns out that lighting R1+R2 were fabricated, presumably from Zs-Ze.
Half the house lighting had open circuit CPC, neatly hidden by a perfect N-E short on the far side of the break. "Zs" values throughout all the fittings were believable, (but not really Zs anyway since no CPC). Very obvious with proper R1+R2, or even with NE IR test done at at far end. (All IR of course was good at consumer unit)