I was asked to look at an intermittent fault in a rental property yesterday:
Apparently over the last month or so, the tenants have several times heard a loud bang, that they think may be coming from the kitchen area of the house (but they are not sure, being elsewhere in the building each time). Until Friday, nothing tripped, but on Friday when this occurred, the MCB for the main socket circuit tripped (first time this has occurred).
One pertinent fact is that approx 2 months ago the central heating was renewed - new boiler, new surface pipes to all the rads - due to the old pipework leaking under the concrete floor. There was a lot of disturbances in the kitchen - units out etc - to get the pipes behind them. The problems have only occurred since then.
The installation has a Memera 2000 CU, most circuits just protected by MCBs, one circuit (not this one) has an RCBO, otherwise there is no RCD protection.
The socket circuit is a RFC on a B32 MCB. I tested the circuit, with no real issues - dead tests at all the sockets I could find - a couple needed their connections tightening to get decent results. IR with everything unplugged & FCUs off measured 90M (L-N), 45M (L-E) and 55M (N-E), stable/repeatable. In summary, the circuit appears in good condition.
If there had been something flashing over, I'd expect carbon deposits etc to give much lower IR results? Unless perhaps a chaffed cable with exposed L copper is touching e.g. a CH pipe, and the cable gets thown away by the force of the flashover, only to creep back and touch again?
With loads connected (as presented), the L+N to E measured at 2.5M. I didn't have time to investigate which load(s) were dragging the IR down.
The kitchen appliances are all built-in, and I've not (so far) been able to remove and check any of them. But I figure if one of them was at fault, it would likely have blown the fuse in its' plug or FCU, and it would no longer work - which is not the case, all the appliances appeared to be working normally. I'm reluctant to start dismantling the kitchen when the tenants are not actually sure that is where the "bangs" are coming from.
Any recommendations on what my next step(s) should be?
Apparently over the last month or so, the tenants have several times heard a loud bang, that they think may be coming from the kitchen area of the house (but they are not sure, being elsewhere in the building each time). Until Friday, nothing tripped, but on Friday when this occurred, the MCB for the main socket circuit tripped (first time this has occurred).
One pertinent fact is that approx 2 months ago the central heating was renewed - new boiler, new surface pipes to all the rads - due to the old pipework leaking under the concrete floor. There was a lot of disturbances in the kitchen - units out etc - to get the pipes behind them. The problems have only occurred since then.
The installation has a Memera 2000 CU, most circuits just protected by MCBs, one circuit (not this one) has an RCBO, otherwise there is no RCD protection.
The socket circuit is a RFC on a B32 MCB. I tested the circuit, with no real issues - dead tests at all the sockets I could find - a couple needed their connections tightening to get decent results. IR with everything unplugged & FCUs off measured 90M (L-N), 45M (L-E) and 55M (N-E), stable/repeatable. In summary, the circuit appears in good condition.
If there had been something flashing over, I'd expect carbon deposits etc to give much lower IR results? Unless perhaps a chaffed cable with exposed L copper is touching e.g. a CH pipe, and the cable gets thown away by the force of the flashover, only to creep back and touch again?
With loads connected (as presented), the L+N to E measured at 2.5M. I didn't have time to investigate which load(s) were dragging the IR down.
The kitchen appliances are all built-in, and I've not (so far) been able to remove and check any of them. But I figure if one of them was at fault, it would likely have blown the fuse in its' plug or FCU, and it would no longer work - which is not the case, all the appliances appeared to be working normally. I'm reluctant to start dismantling the kitchen when the tenants are not actually sure that is where the "bangs" are coming from.
Any recommendations on what my next step(s) should be?