Pretty sure you all know by now I like to dream up random scenarios.

So let's say running SWA to an out building, but the consumer unit is a tricky run that would make it difficult to get SWA all the way to it. Would you then run T+E say from the consumer unit, through the external wall to some form of IP rated junction box, and then join the SWA in this external junction box?
 
Pretty sure you all know by now I like to dream up random scenarios.

So let's say running SWA to an out building, but the consumer unit is a tricky run that would make it difficult to get SWA all the way to it. Would you then run T+E say from the consumer unit, through the external wall to some form of IP rated junction box, and then join the SWA in this external junction box?


Best to always avoid joints in a circuit where possible. What is making it so tricky?
 
I did something like this recently. I terminated the SWA into wago box and the took the sheathed inner cores through the wall, in plastic conduit, straight into the back of the consumer unit. I took an earth, from the same terminal I put cpc from the SWA in, back through the conduit to terminate onto the SWA gland banjo.
 
bear in mind that if the T/E from the CU is buried <50mm deep in plaster, it requires RCD protection.
 
4 options:
Run the whole circuit from CU to outbuilding in T&E.
Run the whole circuit from CU to outbuilding in SWA.
Run the exterior part of the circuit in SWA, glanding the SWA into an adaptable box and the interior part of the circuit in T&E.
Run the exterior part of the circuit in SWA, glanding the SWA into an adaptable box with the cores long enough to reach the CU.
Fith option is to use a different cable altogether.
 
If there is an internal ring final circuit could you not extend a leg in a socket, drill through a wall and place an IP rated socket and then SWA from there to have a couple of sockets there (& down rate a Switched FCU for a lighting circuit)?
 
If there is an internal ring final circuit could you not extend a leg in a socket, drill through a wall and place an IP rated socket and then SWA from there to have a couple of sockets there (& down rate a Switched FCU for a lighting circuit)?
you'd need to fit a 13A FCU after the house socket as you'd be adding more than 1 socket on a spur. would be bad design IMO.
 
If the garage socket & outside socket were incorporated as 1 ring final circuit why couldn't you just add a FCU for the lighting to be down rated?
 

Reply to the thread, titled "Another random question" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top