Just seen another question for this weeks competition from sparks magazine to win a Megger socket tester. The question reads.....

Which of the following is not an isolating device?

a) Single pole light switch
b) Double pole switch
c) Plug and socket
d) Triple pole isolator



Seems everyone is putting C. plug & socket as the answer. I have had a look at table 53.4 in the BGB and plug & socket - outlets say suitable for isolation. I just wondered what anyone's thoughts on this are. Am i looking at this wrong (probably).

Thanks :smile:
 
Last edited:
Agree with A.
Isolator should disconnect ALL Live conductors.

A SP light switch would still leave the N connected at the load.



(I think, without checking!!! :) )
 
Second on the list for "Switching Device" in Table 53.4 of BS7671

[h=1]BS EN 60669-1
[/h] [h=2] Switches for household and similar fixed-electrical installations. [/h]

Isolation = NO. Emergency switching = Yes. Functional switching = Yes.


I should read my BGB more often and not ask these silly questions to be honest. Cheers :smile:
 
Agree with A.
Isolator should disconnect ALL Live conductors.

A SP light switch would still leave the N connected at the load.



(I think, without checking!!! :) )
I'll let you off on account of your caveat! ;)

"537.2.1.1: Every circuit shall be capable of being isolated from each of the live supply conductors. In a TN-S or TN-C-S system, it is not necessary to isolate or switch the neutral conductor where it is regarded as being reliably connected to Earth by a suitably low impedance."

I read this as: If you're checking a TT system fitted with SP MCBs, then you can't use these for isolation (but they're ok for ADS and functional switching).

But the question arises: should DP MCBs (rather than SP) be used on TT systems? :)

(also, agree with everyone, "A")
 
Last edited:
I'll let you off on account of your caveat! ;)

"537.2.1.1: Every circuit shall be capable of being isolated from each of the live supply conductors. In a TN-S or TN-C-S system, it is not necessary to isolate or switch the neutral conductor where it is regarded as being reliably connected to Earth by a suitably low impedance."

I read this as: If you're checking a TT system fitted with SP MCBs, then you can't use these for isolation (but they're ok for ADS and functional switching).

But the question arises: should DP MCBs (rather than SP) be used on TT systems? :)

(also, agree with everyone, "A")

for D/P isolation on a TT earthing system you have a D/P main switch ( often a S type RCD.)
 
for D/P isolation on a TT earthing system you have a D/P main switch ( often a S type RCD.)

Yes you do! :) You're right, of course.

I was wondering about the implied meaning. If "Every circuit shall be capable of being isolated," does that not mean you should be able to isolate every circuit? And if, in order to isolate a circuit on a TT system, you have to disconnect the N as well as the L, surely that means that you should have devices capable of acting as isolators on every circuit (ie DP MCBs or RCBOs)?

(A simple "no" will suffice; I am also amenable to a certain degree of p!ss-taking for overcomplicating things!) :)
 
Second on the list for "Switching Device" in Table 53.4 of BS7671

BS EN 60669-1


Switches for household and similar fixed-electrical installations.



Isolation = NO. Emergency switching = Yes. Functional switching = Yes.


I should read my BGB more often and not ask these silly questions to be honest. Cheers :smile:

Post away mate, ive just learned something i didnt know before that i wouldnt have if you hadnt posted it up :icon4:
 
Second on the list for "Switching Device" in Table 53.4 of BS7671

[h=1]BS EN 60669-1
[/h] [h=2] Switches for household and similar fixed-electrical installations. [/h]

Isolation = NO. Emergency switching = Yes. Functional switching = Yes.


I should read my BGB more often and not ask these silly questions to be honest. Cheers :smile:
Slim this is exactly why the trainee section exists so that you guys can ask whatever you want without fear of being mocked.
This goes for all Trainees this is a safe haven for people to learn, do you think all us old farts were born and instantly knew everything.
 
Slim this is exactly why the trainee section exists so that you guys can ask whatever you want without fear of being mocked.
This goes for all Trainees this is a safe haven for people to learn, do you think all us old farts were born and instantly knew everything.

This is stuff i have covered in college already. I am finished college and now just need NVQ3 and AM2. Just needed to have another look and get the brain working again as it was a while back.

I would never hesitate to ask any questions in here as the mentors are all sound and what one of us knows another may not so could potentially learn something.

This section has helped me a lot since i joined and is a good laugh.

A big thanks to everyone for there useful input here :shades_smile:
 

Reply to Another Sparks Magazine comp question! in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top