mgnelec09
Hi There,
We have just been testing a job that is coming to a close.
The job is a detached bungalow out in the sticks.
The supply comes down overhead lines then down the column, then underground into the property.
Im pretty sure its a PME system.
My end to end readings on the ring mains are pretty normal and R1+R2 also.
My Zs readings on all 4 ring mains are pretty high.
all reading around the 1.00ohms mark although some of them are up to about 1.5 Ohms.
My ZE reading at the supply is 0.47 Ohms
I rang Niceic Technical advise as I wasnt happy with the readings knowing that they need to be under 1.15 for a type B 32A breaker.
The guy told me I need not worry as long as it is protected by an Rcd, and as long as the RCD tripping times are ok.
He then went on to say that it can be anything upto 6000 Ohms!!!!!! Can some one explain wot hes going on about!
Cheers
We have just been testing a job that is coming to a close.
The job is a detached bungalow out in the sticks.
The supply comes down overhead lines then down the column, then underground into the property.
Im pretty sure its a PME system.
My end to end readings on the ring mains are pretty normal and R1+R2 also.
My Zs readings on all 4 ring mains are pretty high.
all reading around the 1.00ohms mark although some of them are up to about 1.5 Ohms.
My ZE reading at the supply is 0.47 Ohms
I rang Niceic Technical advise as I wasnt happy with the readings knowing that they need to be under 1.15 for a type B 32A breaker.
The guy told me I need not worry as long as it is protected by an Rcd, and as long as the RCD tripping times are ok.
He then went on to say that it can be anything upto 6000 Ohms!!!!!! Can some one explain wot hes going on about!
Cheers