mgnelec09

Hi There,

We have just been testing a job that is coming to a close.

The job is a detached bungalow out in the sticks.

The supply comes down overhead lines then down the column, then underground into the property.

Im pretty sure its a PME system.

My end to end readings on the ring mains are pretty normal and R1+R2 also.

My Zs readings on all 4 ring mains are pretty high.

all reading around the 1.00ohms mark although some of them are up to about 1.5 Ohms.

My ZE reading at the supply is 0.47 Ohms

I rang Niceic Technical advise as I wasnt happy with the readings knowing that they need to be under 1.15 for a type B 32A breaker.

The guy told me I need not worry as long as it is protected by an Rcd, and as long as the RCD tripping times are ok.

He then went on to say that it can be anything upto 6000 Ohms!!!!!! Can some one explain wot hes going on about!

Cheers
 
if it's PME then your Ze is way over the max. of 0.35 for a start... with RCD protected circuits, your max. Zs is 1667 ohms as then the RCD will act as fault protection should the Zs be too high to trip the OCPD within the 0.4 secs.
 
I'm no expert in testing so please correct me if I'm wrong but:- R1+R2 = 1 Ohm, Ze = 0.5(rounded) and your getting a Zs of 1.5. What's the problem?

With an rcd you can have up to 1667 Ohms (dont know about 6000 Ohms or is it 6KA that he told you?)

Ok lads I might be wrong off the top of my head, please say so if I am so I can learn where I'm going wrong.
 
I'm no expert in testing so please correct me if I'm wrong but:- R1+R2 = 1 Ohm, Ze = 0.5(rounded) and your getting a Zs of 1.5. What's the problem?

With an rcd you can have up to 1667 Ohms

I've just re-read the op, pme? Overhead supply in the sticks? Readings are high for a TN system but very low for a TT, need to know.
 
Thanks telectrix, should I record the exact readings on the test sheet? with it being overhead lines would it be a TT? I know a TNC-s goes upto about 0.8 ohms. the cable got jointed as the house was being re-built and moved about 3 metres by an old elecy board specialist. I wasnt there when he did it. could this have any influence on the reading? The resin joint looked ok.

Is there a reg that says about high values and Rcd protection? And is the 1.15 for a type B 32amp only for non rcd protected circuits?
 
Last edited by a moderator:
first thing is to measure PSCC and PEFC. if they're the same it's PME (TNC-S). it's TN-S that can be up to 0.8.and as paul says. need to know what it is. guessing is for morons on family fortunes.
 
Last edited:
By the sounds of it, it's more than likely to be TT in which case your Zs can run up to 1667 as others have said. The difference is that you MUST have RCD protection on all circuits to compensate.

See Reg 411.5 and table 41.5

A property I went to a little while ago was fed off a pole with a PME stamp on it, but it was still TT at the house end - guess someone was being a cheapskate with the cable when it all got built!
 

Reply to ANOTHER WEIRD ONE!!!!High ZS readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
896

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
383
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
882

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top