I realise coding for EICR's can be quite judgemental and theres quite a few discussions on them but I was hoping for a bit of reassurance/advice with the following (I have not yet written the report):
1. I feel this would be a C2, my reasoning is that its a great big hole with live conductors visible?
[ElectriciansForums.net] Another 'which code for EICR'.. [ElectriciansForums.net] Another 'which code for EICR'..
2. C2 as live parts visible on 230V side of transformer and just taped up:
3. Broken part on MCB.. C2? I feel less certain about this one. The MCB functions.
4. Main Bonding disconnected to gas.. C2.. All gas pipes tested for continuity to MET and all had continuity.
5. Main bonding not found for incoming water although water pipes showing continuity to MET. Only 1 bonding conductor in MET (10mm). The only 10mm in the house I could find was the one in the second picture bonding this random pipe in the house and then disappearing into the wall. Really not sure what to code this? The main bonding should be within 600mm and its easily accessible to do this, however the incoming pipe is plastic, but then immediately copper once in the property.
6. The consumer unit is absolutely packed and coated with dirt/plaster dust and I can hear it in the RCD and MCB mechanisms as I switch them (all functional though... for now!) Also getting poor IR results on L-E when conductors are all connected and MCB closed (0.08MΩ). When MCB's open (individually)this increases to over 10MΩ for all circuits, so perhaps plaster/grime etc making connection from busbar to E? 'Further investigation and/or consumer unit change C3 (maybe C2)
Sorry for this lengthy one, I've done a handful of EICR's and have felt confident with the coding so far but not so much with this one!!
  • [ElectriciansForums.net] Another 'which code for EICR'..
i'd tend to agree with your codings there. maybe a C2 for the crap in the CU as you have no way of determining if the operation of the MCBs on overload is compromised by the grit etc.
Hi,
Don't do a lot of Domestic myself, but I would concur with your readings, and Tel ; I like your thoughts on the dust/grit.
Regards.
depending on where the location of the transformer is its boarder line C1 for me, exposed fuse , hate those qoe boards exploding rcbo's [ElectriciansForums.net] Another 'which code for EICR'.. all i did was press the test button and this happened C2 on them if they dont trip with my tester lol
I do like the way you spot these things.
I'm guessing you don't charge ÂŁ50 for an in and out report. lol
No.. Just a bit more than that Murdoch :smiley2: (this one was ÂŁ150), but I was there for 7 hours (plus another 2 writing up the report and covering letter with quotes). This particular house was extremely messy!
It looks like the 10mm loops at 'random pipe' and perhaps continues to disconnected gas clamp. Was thinking C3 for JB until I realised it's under the units!
Just about to ask where the jb was
Sorry, should have been more clear. Both the transformer and JB are on top of the kitchen cabinets, with lots of junk stored around them.
C2 for potential danger in my book, leaning towards a C1 if customer is likely to be poking around up there.
Do you not use a software package to do this for you?
No I dont, I only do around 1 every couple of months. If I start doing more I would look at a software package to speed things up as I do take a while getting all the paperwork together.
Reply to Another 'which code for EICR'.. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
loz2754
L
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...