hi guys. am doing my 2392 at the mo and am a bit confused.

for the Zs test does all bonding and earthing need to be in place or do you disconnect the bonding for extraneous parts?

my tutor told me (and therfore in my notes i have) that you disconnect the bonding for the water and gas pipes as you will send a small current through this bonding and therefore could shock someone in a real life situation.

but i've just read in a book that in order to do the Zs test it says "ensure all earthing and bonding is in place"


so which is it?
 
When Zs is measured it is done so under "normal service conditions" i.e all bonding connected.

Ze is measured with the main earthing conductor disconnected.
 
cool. thanks guys.

what about during IR test. we've been told to do the insulation resistence test between the earth block and nuetral block in the CCU to the tops of the breakers.

i'm sure the tutor said that water and gas pipe bonding has to be off for this test too. in 3 years of college this is the first time this has been said to me. is this correct?
 
Last edited:
i'm sure the tutor said that water and gas pipe bonding has to be off for this test too. in 3 years of college this is the first time this has been said to me. is this correct?


You dont have to disconnect the bonding to do this test. However as it's a dead test it is safe to remove them so cant really say he's wrong, it's just a bit uneccessary.

If you do disconnect, then you have to remember to put them back too.
 

Reply to another Zs question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
693
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top