Did a pir to day and found the shed was fed from a 16 mcb in the fuse-board in the house then wired in swa to a rcd in the shed then to a socket.

Now this doesn't feel right but cant find a reason why not
you can isolate the socket by using the the rcd locally or at the house the cables protected by the mcb ans as it swa that's fine
 
I know regulation 433.2.1 specifies that where a reduction in CSA or method of installation, type of cable or conductor, or enviromental change, then overload device should be fitted. I suppose there could be a point argues on several of those cases.

But I agree with you Tel as long as the cable either the SWA or the cable after the RCD can carry 16amps then reg 433.3 can be used.
 
that's why i asked about the size of the SWA. i would have thought it would be 2.5mm coming off a 16A. if it is, then the circuit shouls all be 2.5. as long as the socket ain't wired in alarm cable!!!
 
Yes its 2.5 and i was just having a bad day.I would of put a 16a mcb with the rcd and a 20a mcb in the house but like your say everything is covered, the overcurrent is provided by the 16amp mcb at the house end.
 

Reply to anouther pir question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Replies
13
Views
1K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
520

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top