I'm struggling to understand the answer to this question....

A ring circuit is 54 metres long and is wired in 2.5/1.5 Thermoplastic cable. The Ze for the installation is 0.24Ohms. Cable resistance is 19.51 mOhms per metre. Calculate the Zs for the circuit?

I'll reveal the 'book' answer, once I have had a couple of responses, but I just want to see if others come up with the same (wrong) answer I did. That way I'll know its less me getting it wrong, and more a poorly worded question.

Cheers
 
R1+R2 = (19.51 * 54/1000) /4 = 0.26 Ohms

Zs = .24 + .26 = 0.5 Ohms

or
Zs = .24 + (.26*1.2) = 0.552 Ohms at 70C operating temperature.
 
Last edited:
R1 + R2 = (r1 + r2) Ă· 4

r1 + r2 = (19.51 ÷ 1000) x 54 = 1.05Ω

R1 + R2 = 1.05 ÷ 4 = 0.26Ω

Zs = Ze + (R1 + R2)

Zs = 0.24 + 0.26 = 0.5Ω
 
Last edited by a moderator:
A ring circuit is 54 metres long and is wired in 2.5/1.5 Thermoplastic cable. The Ze for the installation is 0.24Ohms. Cable resistance is 19.51 mOhms per metre. Calculate the Zs for the circuit?
That's an ambiguous term IMO - is that the resistance of the line conductor, or the R1+R2 value, as, if I remember correctly, it's listed in the OSG?

Update:
According to the OSG, 19.51mΩ/m is the value for R1+R2 of 2.5/1.5.
 
Last edited by a moderator:
Ok, time for the book answer...

0.5 ohms

54 X 19.51 / 1000 = 1.05 ohms

1.05 ohms /4 = 0.26 ohms

Add 0.26 ohms to Ze of 0.24 = 0.5 ohms

Now the thing that threw me, even though I had read about it when studying Ring Final Circuit testing is the division by 4.
I understand the concept of half the length, double the CSA etc, but not how that applies in this context.

I understand that you divide by 4 because you have cross connected the ends of the ring, but as that has not been done in this case so why do you still divide by 4?

Sorry if this is blindingly obvious, and I am missing it. Maybe as someone has already said, it's a bit too deep for a Friday.

The book this was taken from is:

Chris Kitcher's Practical Guide to Inspection, Testing and Certification, Appendix C, Question 2.

Cheers
 
Last edited by a moderator:
Ok, time for the book answer...

0.5 ohms

54 X 19.51 / 1000 = 1.05 ohms

1.05 ohms /4 = 0.26 ohms

Add 0.26 ohms to Ze of 0.24 = 0.5 ohms

Now the thing that threw me, even though I had read about it when studying Ring Final Circuit testing is the division by 4.
I understand the concept of half the length, double the CSA etc, but not how that applies in this context.

I understand that you divide by 4 because you have cross connected the ends of the ring, but as that has not been done in this case so why do you still divide by 4?

Sorry if this is blindingly obvious, and I am missing it. Maybe as someone has already said, it's a bit too deep for a Friday.

The book this was taken from is:

Chris Kitcher's Practical Guide to Inspection, Testing and Certification, Appendix C, Question 2.

Cheers

Divide by 4 because at the furthest part of the ring you have "double" the copper back the start and hence why you divide by 4 and not by 2

Hope that makes sense!
 

Reply to Answers on a postcard please... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top